Non-barrier pex suppling Buderus panel radiators
solradman
Member Posts: 58
I looked at a job today where the home owner was completing an addition needing 4 new Buderus panel radiators to heat a bonus room above a garage. The plumber that installed the system (retired and moved away) ran 3/4" pex from the mechanical room to a 4 port manifold and 1/2" pex to the radiator locations using non-barrier pex, When I pointed this out he stated the existing top floor rooms all have panel radiators and were plumbed the same way. The system has been running for over 6 years with no problems. Boiler and plumps are stainless steel, all near boiler piping and components are copper or brass. Main floor is in-slab radiant. Anybody seen or had experience with non-barrier pex in a system like this with Buderus panel radiators?
0
Comments
-
I have one non-barrier job where the Runtal radiator developed a hole and had to be replaced.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
-
A chemical regiment could deal with that also. Probably a yearly boost would be needed. Rhomar hydronic conditioner work well on non barrier systems. They put a thin protective layer on all the insides of the system pipe, boiler, radiator, etc. Also an oxygen scavenger is in the package. That is what gets consumed and requires boost occasionally.
or separate those loops with a HX, additional circ and expansion deviceBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
I've seen pinholes develop in steel panel rad using non-barrier pex in under 3 years.0
-
This LLH was installed on a high temperature, early version rubber hose, system, about 18 months later it had a pin hole. Pretty corroded inside also.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream2 -
I guess the short answer is that it depends. I have systems that have old polybutylene tubing installed with radiant tubing with no issues. But, radiant is at a lower temperature which makes a big difference with oxygen corrosion.
I would think with all of your parts being non ferrous, you shouldn't have much of an issue, but I would put in boiler treatment just to be on the safe side.
Rick0 -
But the tubing now buried in the structure to the emitters is non-oxygen barrier. The part that needs to be isolated with the hx is directly at the end of the tubing.hot_rod said:
or separate those loops with a HX, additional circ and expansion device
I'm never a fan of copper baseboard, but that might be your best option here.1
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements