Adding a Tekmar 360 mixing control
Options
MathewBraun
Member Posts: 2
I’m adding a 4way motorized valve with a Tekmar 360 mixing control. I added mainline circulator off of a cast iron boiler and have a Tekmar 306P switching relay that operates 6 zoned circulators. The question is how do I wire the 360 to the 306p? Much thx.
0
Comments
-
The 306p has an "XX" terminal designed to call the boiler for heat. Terminals 1 and 2 on the 360 should be connected to the XX on the 306p and terminals 7 and 8 should be wired to the boiler. Here is where it gets sticky, terminals 1 and 2 need to be powered and the XX terminals is just a switch. You need to find a power source (preferably 24 VAC) for that circuit.
https://www.watts.com/dfsmedia/0533dbba17714b1ab581ab07a4cbb521/81379-source/306p-d-04
https://www.watts.com/dfsmedia/0533dbba17714b1ab581ab07a4cbb521/42852-source/360-d-06
"If you can't explain it simply, you don't understand it well enough"
Albert Einstein2 -
Much thx Zman!0
Categories
- All Categories
- 85.7K THE MAIN WALL
- 3K A-C, Heat Pumps & Refrigeration
- 49 Biomass
- 418 Carbon Monoxide Awareness
- 71 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.2K Gas Heating
- 92 Geothermal
- 149 Indoor-Air Quality
- 3.2K Oil Heating
- 59 Pipe Deterioration
- 847 Plumbing
- 5.8K Radiant Heating
- 371 Solar
- 14.5K Strictly Steam
- 3.2K Thermostats and Controls
- 50 Water Quality
- 38 Industry Classes
- 47 Job Opportunities
- 15 Recall Announcements