Thermostat well
Dathis
Member Posts: 6
I replaced a thermostat well on 4 inch copper domestic hot water line just 14 months ago, It was a pure brass Winters well, the original was a Weiss that failed in the same way but had been in place for years and was only noticed when thermostat was getting replaced. The well both times has looked like this,, any thoughts on what may cause this so quickly?
0
Comments
-
-
City water in Alexandria Virginia, I'm considering bottling it as an etching compoundEdTheHeaterMan said:What are you measuring the temperature of? Sulfuric Acid?
1 -
They do make them in Stainless Steel.Crap Brass or water issues. City water, contact them and ask them what’s up?0
-
Softened water with a pumped DHW return? Appears to be dezincification. Are these these wells LF brass? I would check the grains per gallon of hardness, had two hospitals with the same problems with t-stat wells and thermostatic mixing valves. Ended up being the water softening contractor increased the pounds per regeneration on the control so they could sell/ deliver more salt. Once decreased to where the grains per gallon was around 3-4 the maintenance nightmares went away. Copper Development Association can be a source of useful information as well. Hope this helps you find a solution to the problem2
-
Yes they are Lead Free brass, I hadn't thought about dezincification, there is no water softener system, but the city water does tend to run closer to 8 on the PH scale and the water temps average 140-150 both of which are known to accelerate dezincification, I will probably follow @pecmsg advice and have them invest in stainless steel thermowells going forwardBenDplumber said:Softened water with a pumped DHW return? Appears to be dezincification. Are these these wells LF brass?
0 -
The hotter the water the more aggressive, and more mineral precipitation .
At some point a strap on temperature gauge makes more sense. I feel they are as or more accurate if insulated. Many precise controls use strap on thermistors, tekmar for one.
With a well type you have to transfer through the well wall and through the wall of the probe. Assuming it was installed with transfer grease🥸
With strap on pipe to thermistor is faster, less thermal lag.
With that much sediment I suspect it wasn’t reading too accurately?
Winters and others have digital strap on gauges.
velocity can take them out, electrolysis also. That looks like hard water. Check the bottom of the water heaters for example if sediment make up.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
Hi @Dathis , I agree with Hot Rod. There could be a degree of galvanic corrosion going on, with all the exposed copper chewing on the brass. Unless you can find a copper thermostat well, I like the idea of going with a strap on sensor. Stainless can be a little or a lot noble to copper, so the wrong stainless well could damage the copper.
Yours, Larry0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements