Blowdown for residential boiler procedure?
Scott216
Scott216 Member Posts: 13
I'm redoing my near boiler piping. I'm going to have ball valves on the risers and wet return so I can isolate the boiler from the system to do blowdowns. I have a residential boiler - Peerless 63-04. What's the procedure for doing a blowdown on a boiler like this? I know I'll need to close those valves and turn the boiler on. But I've heard the pressure should be higher. If so, what PSI should I go to? Do I need to override the pressuretrol or just crank it to the highest setting? I have a hot water garden hose rated at 180F, (McMaster 6285T29) that I can connect to the boiler drain and then go into my basement sump pump.
  • JUGHNE
    JUGHNE Member Posts: 11,623
    Is your sump pump plastic or cast iron?
    Jamie Hall Member Posts: 27,675
    no need to go over 2psi, but if you have a vapourtrol you'll have to isolate it (should have a valve... some even do!)
  • Scott216
    Cast Iron
    EdTheHeaterMan Member Posts: 12,633
    You need to isolate the pressure control or jumper the terminals so when the contacts open, the circuit to the burner is not interrupted. Changing the adjustment is never a good idea. Sometimes you never get it back to where it was before you changed it.