20 year-old Emerson blower motor in Carrier oil furnace/AC
rgar98
Member Posts: 59
in Oil Heating
Hello,
I'm trying to get a blower motor for this 20 year old system. The current Emerson 1/3 hp/115V/1075 RPM blower motor works but I'm anticipating having to replace it. Warning label on blower housing says: CHANGE EXCLUSIVELY:
with Emerson K55HXMSR-5950 but I can't find it. However, I found a Carrier HC41AE117 (Amazon) with same specs.
Suggestions?
Thanks a lot.
Richard
I'm trying to get a blower motor for this 20 year old system. The current Emerson 1/3 hp/115V/1075 RPM blower motor works but I'm anticipating having to replace it. Warning label on blower housing says: CHANGE EXCLUSIVELY:
with Emerson K55HXMSR-5950 but I can't find it. However, I found a Carrier HC41AE117 (Amazon) with same specs.
Suggestions?
Thanks a lot.
Richard
0
Comments
-
Emerson wants you to buy Emerson. Carrier does not care. And the blower wheel does not need know the name brand of the blower motor. Just tell the wheel it is an Emerson, then put any brand on there. Blower wheels never look at the motor. They only look at the direction the air is blowing
This one should work fine. https://www.homedepot.com/p/Mars-1-5-in-3-4-in-HP-Multi-Horsepower-Direct-Drive-Blower-Motor-10466/318552613Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
1 -
Thanks ED.I figured as much, but I'm uncertain b/c the Carrier specs I mentioned were told to me by a vendor online and I'm not certain that they are accurate.
Thanks for the comment and remember that:
"You don't need a weather vane to know which way the wind is blowing."0 -
https://kpaulindustrial.com/regal-beloit-em3585-economaster-1-3-hp-1075-rpm-3-speed-115-volt-direct-drive-blower-motor.html. this is one that might work also
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
@rgar98
Blower motors are pretty generic. As long as you match up the frame size is most important, hp voltage # of speeds and direction of rotation etc.
Don't install a motor rated for less amperage than the original motor.
The OEMs sometimes pay games with their ratings0 -
especially find one that is rated as the same or higher current draw. it is probably more that the old motor is producing a bit more power than rated than the new motor is more efficient. I might go with a 1/2 hp replacement in place of a 1/3 hp oem. I'd also look for ball bearings in the new motor. It is likely that the amount of air in a blower application allows them to run it at a bit more current than rated without overheating but it is better to avoid that situation.0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements