Secondary probe type LWCO for Burnham MegaSteam?
Rusty2
Member Posts: 70
I was wondering if anybody put a Secondary (back-up) probe type LWCO wired in series with the Primary probe LWCO and the Pressuretrol on a Burnham MST. If so where did they put it? On the equalizer? Are there any photo's of this? The Primary would be automatic with the Secondary having a manual reset for safety.
0
Comments
-
Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes1 -
Do you see where you can put the second LWCO? John has done research to illustrate exactly what you need to do here and provided a picture of one of his jobs.JohnNY said:
I'm wondering if everyone else sees what I see.
This is the picture I see on @JohnNY's post
But when I posted the Quote the picture came up different, actually showing a different page in the IO manual and a photo.
Edit: just refreshed my page and John's post updated with the same picture and diagram as the one in my "Quote" post. This is spooky!Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
EdTheHeaterMan said:JohnNY said:
But when I posted the Quote the picture came up different, actually showing a different page in the IO manual and a photo.
Yeah, it took me a couple tries to get this right. I'm learning...Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes0 -
@EdTheHeaterMan
Yeah, it took me a couple tries to get this right. I'm learning...Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes0 -
Thanks JohnNY and Ed. It looks like the Steam Max has different tappings than the MegaSteam. I don't see a place to put another LWCO probe on the MegaSteam unless the Secondary could somehow come off the bottom of the gauge glass.0
-
The 3/4" tapping on the front marked C is for the LWCO as indicated in the key list below the illustration. . There is a 1" tapping in the rear, an inch or 2 below that marked K. This is a great place to install the probe for a secondary LWCO. I would mount the probe there but run a wire from the probe to front and mount the actual control box with the reset button somewhere near the primary LWCO so it is easy to find.
That is how I might do it. You don't want to hide that thing in the rear where no one can find it. That is a 3 hour service call in 10 years when that manual reset LWCO trips and you send 3 rookies to find the problem because the original installer retired a year before, and isn't around to tell them that the reset button is around the back.
Just a thought.
Edit: Here is the key for that illustration
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
1 -
Oh! Sorry. I read that as Steam Max and not the Mega Steam.Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes0 -
Thanks Ed. I didn't think about the tappings on the back. Since I'm not using a water heater the 1" tapping "K" should be perfect.0
-
I agree with @EdTheHeaterMan on "K" possibly "L" why not call Burnham and ask them since their drawing show no height above the water line or the floor0
-
I think you will have trouble with "K" and the flue pipe.
Once we tried to do this using a Hydrolevel 711. But we couldn't get it to work because the gauge glass on the MegaSteam is too short. But maybe someone else could figure out how to do it...
New England SteamWorks
Service, Installation, & Restoration of Steam Heating Systems
newenglandsteamworks.com0 -
I think this is a great idea if the opening for the control is at least 1-1/2" above or below the existing LWCO opening. If they are too close together, then you may get false manual reset tripping. That is never a good thing.New England SteamWorks said:I think you will have trouble with "K" and the flue pipe.
Once we tried to do this using a Hydrolevel 711. But we couldn't get it to work because the gauge glass on the MegaSteam is too short. But maybe someone else could figure out how to do it...
Regarding the K tapping, if you use it for the probe only and run a long sensor wire from the probe to the front of the boiler to an easy to see location, then the vent pipe should not be an issue.
Mr .EdEdward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements