Fluctuating Head pressure on ac unit?
Thanks
Boiler Lessons
Comments
-
-
@mattmia2 Did not check the superheat The Manufacturer said to use sub cooling because of txv it is a micro channel condenserRay Wohlfarth
Boiler Lessons0 -
It’s definitely correct to charge using sub cooling, but superheat will tell a lot about how the system is actually functioning. I’ve seen some odd things with micro channel coils but not specifically what you have going on. How long did it run before the gas was removed? I’m wondering if the expansion valve closing was causing the spike. It would be good to check that the txv bulb is attached well if you haven’t done that already.2
-
Yeah, you really need to know what the superheat is. It's always important just with a TXV you go by subcooling to charge because you expect the superheat to be controlled by the txv. But you don't know what's going on unless you check it.
How is the txv installed? Is the bulb installed correctly? Is the TXV the proper size? Is it an adjustable txv?
After rereading it sounds like the superheat was likely too low and the valve was trying to keep it reasonable.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
I have seen units do that and run fine. The fact that the head rose when you added gas is telling you the condenser is full because when you added more gas you flooded the condenser and drove the head up.
I would check the superheat but a TXV can't make high head pressure. The TXV is feeding based on your 40 degree evaporator.
The only other thing I can think of (and this would be true of only microchannel coils) is if one or a couple of the channels is blocked.
Maybe there is enough room to get temp readings on the individual microchannel0 -
How much of that 100' line set is running thru an attic?
There was an error rendering this rich post.
0 -
On longer line set the sub cooling should be checked at the liquid line in the attic being a decent amount of sub cooling occurs as the liquid stacks in line it tends to get additional sub cooling which when taking your readings at the unit will tend to make you over charge . With micro channel they seem extremely sensitive and seem to be over charged pretty easy . I personally stay away from the micro channel being I be replaced a few that where only a few years out of warranty when they stated leaking at the bottom .i love the idea and from units I ve worked on they seem to not take much of a charge being they condense liquid extremely well which is there up side but the down side is that the bottom 1/ 3 of the coil does not have the same volume as w a copper condenser cool which I feel may be why they over charge so easy . I know from the micro I have charged that I really had a wait for my pressures to level out before adding even the tiniest amount of refrigerant as said they tend to go from on the money to over charged in no time flat . Peace and good luck clammy
R.A. Calmbacher L.L.C. HVAC
NJ Master HVAC Lic.
Mahwah, NJ
Specializing in steam and hydronic heating1 -
Thanks everyone I will be going out today. Now the customer called and said the coil is frozen Will be interesting to see what the solution is
Ray Wohlfarth
Boiler Lessons0 -
Microchannel coils hold little refrigerant. That is why the MFGs state you can't pump down a condensing unit with a microchannel coil0
-
EBEBRATT-Ed said:
Microchannel coils hold little refrigerant. That is why the MFGs state you can't pump down a condensing unit with a microchannel coil
Many manufacturers claim you can't pump down a unit with a scroll compressor either which is completely B.S. if done carefully.
I know little to nothing about microchannel, so I have no idea other than often when a manufacturer claims something it's to cover their butt under all conditions.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
Pictures of the TXV bulb installation and please get us SH and SC numbers.RayWohlfarth said:Thanks everyone I will be going out today. Now the customer called and said the coil is frozen Will be interesting to see what the solution is
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
I’ve seen as little as 3oz. over charge cause a 3ton micro channel condensing unit’s head pressure to go bonkers just like what you’re experiencing.
Does the manufacturer allow for a 100’ line set with that specific model? As others have mentioned, a long line set going through a hot wall or attic can change the sub cooling. Check it at the c/u and the indoor unit and see if there’s any difference.
Also: what’s your static pressure and cfm per ton? Micro channel coils are sensitive to having proper air flow.
Personally, I think that they’re junk technology and I avoid selling and installing them.
Is this a heat pump or straight a/c? Make and model?Bob Boan
You can choose to do what you want, but you cannot choose the consequences.1 -
Well here is the followup I checked the static pressure of the fan and found the air flow for the 3 ton coil was less than 900 cfm. After opening some closed dampers on the return and replacing the filter, the airflow increased to 1,300 cfm. After that, the pressures seemed to be more stable with a 40 degree coil temperature. We were chased away by a rain storm before we could check superheat and sub cooling. Thanks for all your help
Ray Wohlfarth
Boiler Lessons1 -
I wouldn't allow the customer to run that unit until you can confirm the SH is reasonable.RayWohlfarth said:Well here is the followup I checked the static pressure of the fan and found the air flow for the 3 ton coil was less than 900 cfm. After opening some closed dampers on the return and replacing the filter, the airflow increased to 1,300 cfm. After that, the pressures seemed to be more stable with a 40 degree coil temperature. We were chased away by a rain storm before we could check superheat and sub cooling. Thanks for all your help
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
-
Personally,RayWohlfarth said:We checked it today The SH is 9 and the sub cooling is 10
I feel that's good.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements