Mascot FT Wall-Mount Combi Boiler 199 MBH ERROR 10

Options
Isi
Isi Member Posts: 7
I've had my Combi 199 boiler working fine until about a year ago when it started giving me error 10 once and a while. Sometime it happens once a day and sometime once a week or even 2 weeks. I have replaced main board, the igniter, cleaned the burner, replaced the flame detector and made sure there was no blockage on the vents. Even after all that I keep getting error 10.

Comments

  • GGross
    GGross Member Posts: 1,050
    Options
    Well since you replaced all the parts I'm going to direct you towards the gas supply, as in the gas coming into the boiler. You need to record incoming gas pressure at the appliance, and also check it with everything else that uses gas turned on. Other than that maybe you have a loose wire, but i would start with the gas since it costs no money to fully check that out.
  • Ironman
    Ironman Member Posts: 7,376
    Options
    What the manual say about the E10 code and how to diagnose the problem?
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.