Moving radiators in a converted gravity system
plumb1pa
Member Posts: 10
I've got a customer who wants to move 2nd floor hot water radiators from one room to another. They are fed by a one inch supply and return line (two radiators off one supply and return) can I just cut them out and reroute the piping with 3/4 heatpex? Or do I need to keep the one inch. I'm concerned about flow.
It's an old gravity system that someone else converted I can't see how it works the way the boiler is piped, but he says the heat has been fine. Thanks in advance.
It's an old gravity system that someone else converted I can't see how it works the way the boiler is piped, but he says the heat has been fine. Thanks in advance.
0
Comments
-
If you are concerned about maintaining balance and have no other way to do it, stick with the 1 inch. The difference to 3/4 inch doesn't seem like much, but the latter will have twice the velocity -- and 4 times the head loss.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
Ok, thanks
0 -
Be careful... Keep the runs the same length as before. Gravity systems can be tricky. Dont trap piping... keep the same pitch as before.0
-
agree with jamie. If your adding piping and fittings to move it your also adding head loss to it so reducing size will make it that much worse.0
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 97 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 929 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 42 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements