I've got a customer who wants to move 2nd floor hot water radiators from one room to another. They are fed by a one inch supply and return line (two radiators off one supply and return) can I just cut them out and reroute the piping with 3/4 heatpex? Or do I need to keep the one inch. I'm concerned about flow.
It's an old gravity system that someone else converted I can't see how it works the way the boiler is piped, but he says the heat has been fine. Thanks in advance.

Welcome

It looks like you're new here. Sign in or register to get started.

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 25,958
    If you are concerned about maintaining balance and have no other way to do it, stick with the 1 inch. The difference to 3/4 inch doesn't seem like much, but the latter will have twice the velocity -- and 4 times the head loss.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    kcopp
  • plumb1pa
    plumb1pa Member Posts: 10
    Ok, thanks
  • kcopp
    kcopp Member Posts: 4,546
    Be careful... Keep the runs the same length as before. Gravity systems can be tricky. Dont trap piping... keep the same pitch as before.
  • pedmec
    pedmec Member Posts: 1,197
    agree with jamie. If your adding piping and fittings to move it your also adding head loss to it so reducing size will make it that much worse.