Internal siphon
johnjohn89
johnjohn89 Member Posts: 115
I took photo from steam boiler! What does this internal siphon do? What is name of this gauge? Sensing internal boiler pressure? Why no sensing any pressure when boiler off mode? I am apprentice need to learn more about boiler!
  • pedmec
    pedmec Member Posts: 1,372
    protects the gauge. same as pigtail, which real name is a siphon tube. its internal to the gauge
    EBEBRATT-Ed Member Posts: 20,236
    Yes As @pedmec pointed out you can install it on a steam boiler without a separate pigtail and the gauge will still be protected from steam
    ethicalpaul Member Posts: 8,866
    ...for a few hours anyway!
  • ChrisJ
    ChrisJ Member Posts: 17,414
    Curious if anyone has taken apart one of these internal siphon gauges. I'm curious what's inside.
  • Hap_Hazzard
    Hap_Hazzard Member Posts: 2,919
    It reads zero when the boiler is off because there is no pressure (relative to atrmosphere) in the boiler when it isn't steaming. While the boiler is producing steam, there will be only enough pressure to move the steam out of the boiler, until all the vents close. The the pressure may then increase to a point determined by the rate of vaporization in the boiler and the rate of condensation in the radiators. If the system is well balanced it should only be two to eight ounces in a typical one-pipe residential system, so the 30 PSI range on these gaugeshas nothing to do with the operating rage of the system. It is required to be two times the opening pressure of the relief valve, which is 15 PSI.
  • johnjohn89
    Great! Thank u very much!
  • johnjohn89
    Thank u so much
