Damaging thermostatic steam traps

Robstorms
Member Posts: 4
New user here and pleased to be able to learn from the experts! I have heard authorities say that a stuck open steam trap on a radiator can damage good traps down the line. What is the mechanism that can cause this damage? I think I understand that steam can flow backwards into a good trap, and I would think the high temp would cause it to close but I don't get the damage. Thanks! Rob
0
Comments
-
-
It may damage them, but that is secondary to shutting down steam flow to the other radiators -- making them heat poorly, if at all.
There are, however, lots of ways to damage thermostatic traps. As @mattmia2 says, any water hammer at the trap is lethal. There is a rather delicate bellows in there which does not take kindly to overpressure. Therefore, you also have to watch general overpressure -- one of several reasons why 1.5 to 2 psi is regarded as the maximum differential pressure across the trap (before someone yells -- yes, I know they are rated at 3 psi working. It is not, generally, good practice to run a device right at its working limits all the time).Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
And this will be pronounced when you are using thermostatic radiator valves to control each radiator. With a closed radiator valve and a close thermostatic trap you are going to form a vacuum in the radiator as the steam condenses. As soon as the thermostatic trap opens up, everything will head that way and that's when all **** breaks loose. Thermostatic radiator valves have built in vacuum breakers but they fail like everything else.1
-
Thanks so much for the answers! If I may follow up, easiest way to test thermostatic radiator traps for function? I have a thermal camera and wondered if I could see proper ( or improper operation using that. Thanks! Rob in Rochester, NY0
-
Thermal camera or IR thermometer -- you want to see the outlet of the trap at least 5 degrees cooler than the inlet when the radiator is hot all the way across. But -- doesn't have to be more than that.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
i wonder if anyone knows of a real steam expert within a resonable service call to Rochester New York? ( 2 pipe system, large old 4 apartment house, one boiler). Looking for someone great at troubleshooting/diagnosis. Thanks !!0
-
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting1 -
Thanks!!0
-
I can't think of anyone in that part of New York -- I think we've had trouble finding someone before. You may need to get a copy of The Lost Art of Steam Heating -- if you don't have one -- and make yourself your own expert.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 938 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements