Economite issues.
I noticed the pilot was out so I relit the pilot.
Flipped the switch and I have a pilot and I have a blower but still no flame.
Im guessing the low water cut-off and the pressuretrol must be working since they are allowing the blower to kick on.
Bad gas valve?
Any help is greatly appreciated
thank you in advance.
"The toes you step on today are connected to the butt you'll have to kiss tomorrow". ---Vincent "Buddy" Cianci
Comments
-
-
-
Has anyone done a combustion test on that burner? The E20 is not a flame-retention burner, and the boiler was designed for one.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting4 -
could be the thermocouple0
-
I bet on end switch of burner motor. Just did one day b4 yesterday. Fasco d454 motor. Unless in fact you did not have valve lever in on position.0
-
Steamhead said:Has anyone done a combustion test on that burner? The E20 is not a flame-retention burner, and the boiler was designed for one.
What do you mean by flame retention? It has a horribly designed pilot.Homeowner, Entrepreneur, Mechanic, Electrician,
"The toes you step on today are connected to the butt you'll have to kiss tomorrow". ---Vincent "Buddy" Cianci1 -
tim smith said:I bet on end switch of burner motor. Just did one day b4 yesterday. Fasco d454 motor. Unless in fact you did not have valve lever in on position.Homeowner, Entrepreneur, Mechanic, Electrician,
"The toes you step on today are connected to the butt you'll have to kiss tomorrow". ---Vincent "Buddy" Cianci1 -
Flame retention is a burner design. Like manual transmission or automatic transmission on a car. Just a different design. Flame retention will be more efficient under most conditions and will work better in your boiler. That said, I'm guessing that it has worked fine for some time now so, if it ain't broke don't fix itbrandonf said:
No combustion tests.
What do you mean by flame retention? It has a horribly designed pilot.
But @Steamhead could always find something better to spend your money on!
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
1 -
I bet a combustion test on that burner in that boiler would show elevated CO levels. I've seen the same thing with the E20 and the Wayne P250/P265 in similar boilers. Switching to a burner such as Carlin EZ-Gas or Midco EC series cured the problem. @brandonf , where are you located? Let's get this thing tested.EdTheHeaterMan said:
Flame retention is a burner design. Like manual transmission or automatic transmission on a car. Just a different design. Flame retention will be more efficient under most conditions and will work better in your boiler. That said, I'm guessing that it has worked fine for some time now so, if it ain't broke don't fix itbrandonf said:
No combustion tests.
What do you mean by flame retention? It has a horribly designed pilot.
But @Steamhead could always find something better to spend your money on!All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting1 -
Got it. But are Brandon's and my Economites more like a Mack Triplex or a Muncie Rock Crusher?EdTheHeaterMan said:Flame retention is a burner design. Like manual transmission or automatic transmission on a car. Just a different design. Flame retention will be more efficient under most conditions and will work better in your boiler.
I've heard the term "Flame Retention Burner" often on this forum from you and @Steamhead. I have a lot of questions.- Does it have something to do with the shape and direction of the flame within the combustion chamber?
- What is the history of Midco, the Economite and Flame Retention Burners?
- Were they a better design for some older obsolete type of boiler.
- Easier to manufacture years ago?
- Easier to install back in the day before modern combustion analyzers?
- Something that would run before the advent of computer controls and circuit boards?
I really do appreciate all the knowledge shared on this site. Thank you in advance.
0 - Does it have something to do with the shape and direction of the flame within the combustion chamber?
-
A Flame retention burner (weather oil or gas) uses higher air pressure and increased air velocity to better mix air and fuel. This causes a more compact flame usually with a higher temperature and a cleaner burn.
Flame retention burners are usually noisier.
Older boilers with larger flue passages could operate with most any burner.
Newer boilers with smaller more restrictive flue passages may need the higher static pressure of a flame retention burner to move the combustion gasses through the boiler.
Non flame retention burners may not burn well in a modern boiler3 -
To add to this- the term "flame-retention" describes the way the flame is "locked on" to the firing head. This results in a very stable, compact flame, unlike on an older burner where the flame would "float" in the firebox. It also needs less excess air to produce a clean flame, increasing efficiency.EBEBRATT-Ed said:A Flame retention burner (weather oil or gas) uses higher air pressure and increased air velocity to better mix air and fuel. This causes a more compact flame usually with a higher temperature and a cleaner burn.
Flame retention burners are usually noisier.
Older boilers with larger flue passages could operate with most any burner.
Newer boilers with smaller more restrictive flue passages may need the higher static pressure of a flame retention burner to move the combustion gasses through the boiler.
Non flame retention burners may not burn well in a modern boiler
@WMno57 , the E20 and similar Economites were descended from Midco's "Lo-Blast" conversion burners. These were designed for changing coal-fired boilers to gas, and IIRC were mounted in the ash pit of these boilers. Somewhere I have a brochure describing the Lo-Blast, which I believe also shows some early Economites.
Midco's current model conversion burner is the EC, which should run well in that Peerless.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting2 -
Look, I have an e20 burner and it just keeps running. No matter what I do cannot stop it from blowing unless I turn power off. Could not get pilot light to stay on once I switched to on position. Changed out t-coupler and same thing ? What have I got going on ?0
-
First thing I'd check is the thermostat circuit. A short in this circuit will make the burner run continuously. Disconnect one of the thermostat wires- if the burner stops, that's your problem.hyper1also said:Look, I have an e20 burner and it just keeps running. No matter what I do cannot stop it from blowing unless I turn power off. Could not get pilot light to stay on once I switched to on position. Changed out t-coupler and same thing ? What have I got going on ?
What boiler is this E20 installed in?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements