venting
RWALD
RWALD Member Posts: 23
I Know this is not heating related but I figured its worth a shot. My question is if my shower or sink drain is less than 5 feet from my main sewer line do i still need to vent it?
  • Intplm.
    Intplm. Member Posts: 3,069
    If there are no other fixtures draining from above in the main sewer then maybe not.
    There are single fixture vents called sudor vents, or sure vents that can be used.
    Your local codes and building department can also help with this question.
    Jamie Hall Member Posts: 27,513
    Sometimes. This is called wet venting and in certain conditions it is permitted -- and the conditions differ with codes, so you will need to check whatever code is in force in your area.
  • Larry Weingarten
    Larry Weingarten Member Posts: 4,143
    Hi, thinking just of the physics involved, I'd vent it, with something like a Studor vent, which is a brand of air admittance valve. If there is no vent, than you're trusting that the trap will never have the water sucked from it by a pull from the main sewer line, and that seems optimistic. When the water is pulled from the trap, you'll know because of that hard-to-ignore sewer gas aroma :#
    Yours, Larry
    hot_rod Member Posts: 27,702
    edited April 2022
    another method that was used is called stack venting. All the fixtures on one level were 5’ from a main 3” vertical drain which carried through to the roof. Plenty of air space to vent all the fixtures connected to the “stack”
    It depends on the type of DWV system you have,
  • rick in Alaska
    rick in Alaska Member Posts: 1,525
    On the places using the UPC, you can do it, but it depends on what else is connected to than line, and how the vent its tied in. In short, you can run the 2" line five feet before you have to have a vent on it. But, it depends on what else is going on.
    Rick
  • RWALD
    Thanks guys I'll vent it