Hello. I’m new here and this forum has been excellent in helping me get my dad’s boiler running better.
Just a question on pressuretrol settings: The system seems to vent right at .25 psi (stays there for a while before building pressure) and cuts out at .5 psi. The boiler drops below .25 psi during the delay and builds back up again until Cut-Off (1.5psi). Does this have any negative impact on venting of the radiators?
I’m curious if there is any negative impact of allowing the system to drop below the venting pressure.
I’m curious if there is any negative impact of allowing the system to drop below the venting pressure.
0
Comments
-
Actually this is what you want it to do. This gives the vents a chance to open again, if there is still air in the radiator, and let it out when the boiler fires back up again, so the radiator can heat up more.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Got it! Thank you for the reply.0
-
The standard 0-30psi are notoriously inaccurate, especially near the min or max readings.
If you are really interested and want to fine tune the pressure, or at least observe it in finer detail....find yourself a low pressure gauge. 0-3psi should cover it. You have to keep the 30psi gauge to be code compliant, but you can T off of the pig tail and have dual gauges.
Long story short....for three winters I ignored this advice. Bought a new 0-30psi gauge and was certain I never exceeded 1psi. I installed a 0-3psi gauge and realized I was closer to 3psi, not 1psi. Not ideal at all.
I now have a 0-20oz gauge and have tuned the system to not exceed about 10oz of pressure.0 -
As mentioned many times in other discussions, most low pressure gauges cannot handle a pressure surge to 15psi (relief valve setpoint).
If you insist on keeping a low pressure gauge installed, either get one (like a Magnehelic) that can handle that pressure or install an isolation valve at the inlet to the low pressure gauge.
0
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 927 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements