Steam boiler
Comments
-
How stable is the water line while it is steaming? What does the near boiler piping look like? Much more likely it is being thrown up in to the mains because the boiler is making wet steam than being pushed out the return. Also possible that the return is partly clogged and that usually takes longer to empty the boiler but wet steam is the more likely culprit .1
-
Matt has it. I think I've seen only one or two credible cases of actual verified "slow return" situations on this site, but that's where everyone thinks to go first. Far far more common is the near boiler piping sucking/throwing water up to the mains.
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
I will also ask / add , , ,
what pressure are you running?
and when did you service the pigtail last ?
pictures,
one or 2 distant showing the whole boiler, floor to ceiling, so we can see the piping above,
and a close up or 2 of the Ptrol, gage, sightglass, and LWCOknown to beat dead horses0 -
Some history would also be helpful. Is this a new boiler? If not, when did problem start and was any work done to boiler or to heating system?0
-
A check valve is certainly one of the last things that you want to add to the system0
-
I will take some pictures and post them. The pig tail for the pressure troll was cleaned recently. Also flushed And drained off top of boiler . And add some cleaning chemicals. The water level is normal 3/4 up in the glass at start. The boiler starts you can see some surging in the glass. After running for a few minutes the water slowly reduces in the site glass until it disappears boiler goes off on low water cut off. After a few minutes off the water comes back. and it does the same short cycling over and over. Boiler there's about 10 years old. Boiler has 2" supply supply to a 3" main with equalizer and a heart for loop. It has had some condensate lines near the boiler replaced. There is 2" and a 1/2 newer car newer copper condensate lines coming back to a 2" line At The Hartford loop and in 2" into the boiler .0
-
-
It does have a skimming port which I used to drain about 20 gallons of water out. Added some chemicals to further clean. Still losing water After a few minutes of run. Although after off for a few minutes the water reappears . The water looks clean In sight glass and what was skimmed off the top.0
-
I'll get pictures of the piping and the whole system in the next couple days Thanks for The feedback0
-
It would take a long long long time to boil away all that water into steam. If it drops while you watch it is surging.
also skimming isn’t draining…your use of the terms interchangeably might point to a factor in this, or might notNJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
-
If to much cleaner is added that can cause problems like surging. Drain the boiler completely and fill it up with clean water - no chemicals - and let us know if things change.
Also skimming is a slow process, it takes and hour or two to fill a 5 gallon bucket. If you skim to fast it roils the water and you don't get all the oils that might be floating o top of your boiler water.
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge2 -
Here's some pictures of the boiler and the piping.0
-
-
-
no equalizer is not allowing the header such as it is to drain.
drain flush and skim, the skim water should drain out slow the size of a lead pencil. get rid of the chemicals and then fill it and try it again0 -
I will drain drain the system completely completely again and fill it up with water with no chemicals see how it works.0
-
There is an equalizer up by the ceiling in the 3" pipe, it been there for 80 years or so. It may not be in the exact right spot but there's definitely a 2" pipe connecting the supply to the return.0
-
Oh my.
Is that pipe that will inevitably drip on the burner where you were skimming?0 -
You'd have to screw an extension nipple onto it. No big deal.mattmia2 said:Oh my.
Is that pipe that will inevitably drip on the burner where you were skimming?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
@Mike_h , what model SGO is that?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
I can't identify the equalizer. It might be there, but 80 years doesn't mean anything to me--it could have been piped wrong for 80 years.Mike_h said:There is an equalizer up by the ceiling in the 3" pipe, it been there for 80 years or so. It may not be in the exact right spot but there's definitely a 2" pipe connecting the supply to the return.
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
There may be what you judge to be an equalizer, but when one looks at your piping it isn't where it's supposed to be, and given you are having water loss issues this is something to look at, in addition to what appears to be an undersized header.
I marked up the picture to show where the equalizer is supposed to be, while it's to equalize pressure it is also to make sure any water in the header is immediately returned to the boiler.
That boiler has 2 1/2" tappings in the block and I don't see a size increase at the header so the header is undersized as it's supposed to be 3", this can amplify the water sucking out of the boiler and being thrown out into the system.
I'm assuming everything there is 2 1/2", but can't always tell from photos, if it's only 2" the problem is even worse.
0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements