Is this asbestos? Plus a question about the king valve.
pcolburn2
Member Posts: 25
Is the dark material on the main steam shutoff asbestos?
Also, I’m open for suggestions as to how to deal with the shutoff valve.
It appears to be pinhole leaking from where the bolted elements come together.
Should it be in kind replaced, high heat expoxy sealed or replaced with mains without a shutoff?
This is a one pipe system single boiler system servicing a multi unit building.
Also, I’m open for suggestions as to how to deal with the shutoff valve.
It appears to be pinhole leaking from where the bolted elements come together.
Should it be in kind replaced, high heat expoxy sealed or replaced with mains without a shutoff?
This is a one pipe system single boiler system servicing a multi unit building.
0
Comments
-
-
As @mattmia2 said, the gasket between the flanges can be re[laced but the valve will probably have to be removed to allow for access to the gasket material and the flanges. The gasket will not just slide out to be replaced and the metal gasket surfaces on the flanges and valve will have to be cleaned. This is not a job for a novice or untrained since that valve is heavy and the gasket is usually tough to remove. One more thing, if the steam has leaked for a long time the metal surfaces of the valve and flanges may need to be resurfaced or if they are too badly damaged they may need to be replaced. If I were you I would call a service company to do the work but in my case I was the one that would be called. As far as the question of that material being asbestos, have it tested to be sure.0
-
Is this Brooklyn?Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes0 -
The only way to know is to take samples and have it analyzed. I agree the ceiling needs to be tested as well.0
-
I'd have that stuff tested. Maybe a couple of samples, one of whatever is on the ceiling and one with whatever is on the pipe.
Is it hard as a rock or soft and spongy?
I almost wonder if there was a steam leak and someone put some JB-Weld type substance on it to try and fix the leak, and that stuff on the ceiling is a type of paint to cover up damage from the steam leak.
I've done a couple tests in the past....not sure who I used but I think I got the kits through Amazon. Results were in 5 days with a certificate. I think I paid extra for overnight testing too.0 -
Most likely it is asbestos. I would just chop the old valve out and put a short pipe in it's place unless your local code requires a stop valve
The easiest way to remove/replace that valve is to remove the bolts holding the valve bonnet and pull that out first. Much less weight to deal with0 -
Have the material on the valve tested. And while you are at it, the ceiling material tested for asbestos. Asbestos is usually not a problem unless it is disturbed ["fryable" ]
The valve can be removed and or replaced. New gaskets will repair the leak.0 -
If you have asbestos it can be removed by the glove and bag method.
The valve does not need to be removed to clean the out the old gasket.
The bolts can be removed and the valve allowed to roll down on the one bolt on the bottom of the flanges.
The safest way to do this is to pull the bonnet out of the valve, that takes a lot of weight off the valve body.
The replacement gasket for the bonnet can be made from 1/8" thick Monico graphite gasket material.
This job is a tweo man job. (two men is for safe working conditions)
JakeSteam: The Perfect Fluid for Heating and Some of the Problems
by Jacob (Jake) Myron1 -
The gaskets may also be asbestos0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements