Malleable or Cast Iron fittings?
ranzerox
Member Posts: 52
Sorry to beat this topic to death!
I'm in NYC, what fittings for steam please? I see companies selling near pipe kits and it all looks malleable. I'm thinking malleable. Thanks!
I'm in NYC, what fittings for steam please? I see companies selling near pipe kits and it all looks malleable. I'm thinking malleable. Thanks!
0
Comments
-
Either will work. Stay away from Galv.
Time was, (before that new fangled copper pipe) Cast cost less than malleable. The Gas company did not like the way Cast could crack on impact so they liked the more expensive malleable fitting. Today there is a lot less use for cast so the malleable fittings are near the same cost.
So, if you can get a good deal on Cast for a steam job. Go for it. It can be hard to find at local supply companies.Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
1 -
Cast when availability allows, otherwise malleable out of necessity.gwgillplumbingandheating.com
Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.1 -
Can I use #150 or #300, thanks!0
-
Honestly, I've only seen those ratings for flanges, where load-bearing is critical. As long as you're buying schedule 40 fittings, you should be okay.
BTW, I use maleable fittings because it's easier to get a pipe wrench to bite on them.Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-242 -
-
-
If I go with malleable, which pressure rated should I go with? Here's a picture of a fitting I'm considering using versus one rated for 300. Thanks
0 -
Also, if you use a pipe joint compound with PTFE you'll never have to worry about taking joints apart. I love the stuff.STEAM DOCTOR said:Only real benefit to cast, is that it's easier to crack ( in event you need to remove in the future). In this day and age, with grinders and all sorts of saws and blades, this should not be much of a consideration.
Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-241 -
Interesting. I've never seen a pressure rating on a fitting before. Maybe they were there and I never noticed.ranzerox said:If I go with malleable, which pressure rated should I go with? Here's a picture of a fitting I'm considering using versus one rated for 300.
Since steam systems typically operate at 3 psi or lower, it's not really anything to worry about. The safety valves open at 15 psi, so 300 psi is 20 times the highest possible pressure they could see. Since I'm not a pro, maybe I just haven't seen one break due to pressure, but I'd be really surprised if anybody else has. I'd expect the pipe to split along the weld long before a fitting exploded. I'd say go with whichever is cheapest, all other things being equal.Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-241 -
Standard CI and Malleable fittings are usually not marked with a pressure rating. But it's widely known that Cast Iron has a steam rating of 125# and malleable has a steam rating of 150#. That's all you need for a 15# rated system.
XH cast iron is rated 250 lb and xh malleable (usually called ductile iron) is rated 300#2 -
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements