Boiler water PH
Comments
-
It seems unusual that your boiler water would test that basic. (High pH). First thought is that something is wrong in the testing.If it is a pH of 14, which could happen, by seriously dosing the boiler with a lot of potent base, you could drain it, wash it out and refill.
If it is indeed pH of 14, be careful. Very caustic. The eye is especially vulnerable to base (high pH) splashes. Not good for skin either.Old chemist, not a heating pro.
best wishes1 -
To my knowledge there is nothing in the function of a steam system that will raise the PH like that. In fact the condensate returning will typically have a low PH <7. I use treatment to get my boiler water to ~10-11, but the wet return measures around 5.5.
Getting up to 12-14 is either massive amounts of water treatment or a faulty test strip.
How is the boiler working? I would expect a lot of surging at that PH level.1 -
That’s exactly what I thought as well. I am using a professional grade ph strips that I purchased from a reputable company. However, they could be bad…
I will order some different strips to see if that makes any difference
my water is foaming very bad… in fact, all the way up the sight glass0 -
Curious,erussell58 said:This may be a question more suited to a chemist than anything but here goes…
My boiler feed water is approximately 8.5-9.5 PH. However, when I test the actual boiler water, I get a reading of 13-14. Any guess what may be going on?
What's your boiler water's TDS vs the feedwater TDS?Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
I share KC's thoughts above except for the one about the surging at high PH. My video experiments showed me that high PH (which I achieved via Rectorseal 8-way) had no effect on surging, at least with my new boiler. I had cranked my ph to 13-14 without any surging.KC_Jones said:To my knowledge there is nothing in the function of a steam system that will raise the PH like that. In fact the condensate returning will typically have a low PH <7. I use treatment to get my boiler water to ~10-11, but the wet return measures around 5.5.
Getting up to 12-14 is either massive amounts of water treatment or a faulty test strip.
How is the boiler working? I would expect a lot of surging at that PH level.</p>
Things that I have seen affect it were other water quality issues (oil, possibly dirt, definitely other water treatments) and of course really high water level.NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
-
ChrisJ said: I don’t know the TDS of either but we are sending out water samples to the lab
This may be a question more suited to a chemist than anything but here goes…
Curious, What's your boiler water's TDS vs the feedwater TDS?
My boiler feed water is approximately 8.5-9.5 PH. However, when I test the actual boiler water, I get a reading of 13-14. Any guess what may be going on?
0 -
Is this Steam or Hot water?erussell58 said:This may be a question more suited to a chemist than anything but here goes…
My boiler feed water is approximately 8.5-9.5 PH. However, when I test the actual boiler water, I get a reading of 13-14. Any guess what may be going on?0 -
Derheatmeister said:
This may be a question more suited to a chemist than anything but here goes…
Is this Steam or Hot water?
My boiler feed water is approximately 8.5-9.5 PH. However, when I test the actual boiler water, I get a reading of 13-14. Any guess what may be going on?0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements