Vaporstat
Steve_211
Member Posts: 49
In setting a vaporstat, what is a good, initial setting...and where do you go from there?
0
Comments
-
It's an experiment. You want the cut in as low as possible. You want the cut out just high enough to get the steam to the radiators. To work right you need good steam traps and good venting. That is the secret to kepping the pressure low and controlibel0
-
I swapped out my Honeywell pressuretrol with a Honeywell vaporstat back in September, 2020, I initially set it at 10 ounces with the differential set at 4 ounces. The gauge shows approximately 10 on the cut out and 6 on the cut in. Should the cut out be higher and/or the cut in be lower? I haven't touched it since I initially set it.0
-
If it's heating ok then don't raise the cut out. You could widen the differential if the boiler is short cycling to give it a longer cycle0
-
If you like to burn fuel for fun
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
Not this year with fuel pushing north of $3.50 per gallon.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements