Flush (clean) the wet return
Fmassarotto_9
Member Posts: 148
Hello,
I found the wet return, as many people have suggested i check in the other 4 threads i made. Before we make the strike to call a plumber, is a plumber necessary to clean this. How would i flush/clean it. I will attach some images. Hopefully this could be figured out
I found the wet return, as many people have suggested i check in the other 4 threads i made. Before we make the strike to call a plumber, is a plumber necessary to clean this. How would i flush/clean it. I will attach some images. Hopefully this could be figured out
0
Comments
-
Is the return plugged ?
There was an error rendering this rich post.
0 -
Big Ed_4 said:Is the return plugged ?
the boiler is consuming a lot of water. i'm adding up to a gallon every 3 days. The vents are new the radiators are pitched, a little smoke comes out the chimney but that's normal i heard. i see chimneys smoking every morning going to work. nothing outta the ordinary. i assume it could be plugged based on what i've read on other posts here and on google. If the boiler is off the water level doesn't budge. When the boiler is on the water in the sight glass drops dramatically so i suspect the water isn't coming back
0 -
What type vents ? Always instal good float type vents .I don't feel you have a plugged return . You would know it with a sound of a hammer on start of cycle ,and how much water could it hold ? . Weil McLain boiler uses o-rings to seal it's sections would be my concern if you covered your bases .
There was an error rendering this rich post.
0 -
Big Ed_4 said:What type vents ? Always instal good float type vents .I don't feel you have a plugged return . You would know it with a sound of a hammer on start of cycle ,and how much water could it hold ? . Weil McLain boiler uses o-rings to seal it's sections would be my concern if you covered your bases .
i got vari valves. all radiators. no main vents tho, i looked at all the piping couldn't find them
0 -
If you are adding water at the rate you mention, you have a leak. It is, probably, not a very big leak, and thus it may be hard to find -- but if you are adding water, the old water has to be going somewhere.
All radiator valves. Packing tight? All unios --tight, no drips, no staining? All threaded connections -- no drips, no staining?
Cleaning the wet return -- while always a good thing -- isn't going to help the water loss.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Jamie Hall said:If you are adding water at the rate you mention, you have a leak. It is, probably, not a very big leak, and thus it may be hard to find -- but if you are adding water, the old water has to be going somewhere. All radiator valves. Packing tight? All unios --tight, no drips, no staining? All threaded connections -- no drips, no staining? Cleaning the wet return -- while always a good thing -- isn't going to help the water loss.
idk where the leak could be. the vents have tape and tightened good. everything near the boiler seems to be in order. the only thing i can think of now is it is under the floor, before it reaches the rads. i've checked well with a flashlight. ive shut the boiler down and looked everywhere. idk where else to possibly check
0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements