Should my PVC flue pipe sweat?
bphillips921
Member Posts: 22
in Gas Heating
We built a new home this fall. I noticed this winter when it got really cold (under 10 degrees Fahrenheit) that the PVC flue pipe from my furnace was sweating near where it exits the home. It's in an unfinished basement but the basement is kept at 68 degrees. I assume this is not normal, correct? How can I fix this?
If it matters, it's 2" PVC flue pipe, roughly 25ft long. The furnace is a 70K BTU furnace.
If it matters, it's 2" PVC flue pipe, roughly 25ft long. The furnace is a 70K BTU furnace.
0
Comments
-
One of those pipes should be the furnace’s combustion air intake, and will sweat when it’s very cold outside because its outer surface will be below the dewpoint in your warm basement. This is normal. If it causes a problem, you can insulate the pipe with something that will stand up to moisture, like closed cell foam.—
Bburd3 -
My dad's had frost on it when it was -20F out.
I tried to get him to insulate it but he doesn't care if it drips on the basement floor, so it is what it is.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
Thanks guys! I'm getting ready to finish the basement and hang drywall, so I wanted to get this figured out before that. Is there pipe insulation that big (2 inch)?0
-
Insulation size for that pipe would be for 2" SCH 40 iron pipe or PVC
The pipe is 2 3/8" outside diameter.
I would only insulate it above your SR, leave the rest of it bare and even sweating on occasion. The sweat is produced by heat transfer which will slightly warm up your combustion air going into the furnace, IMO.0 -
Closed cell 2” may be a little expensive and difficult to obtain for a HO. A couple layers of bubble wrap would probably suffice and be less expensive.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
I would leave that vent exposed at best and accessible at least. Im not wild about burying it inside where if there were an issue it would go undetected.0
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 927 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements