Extra drains if doing Pumping Away?
rsilvers
rsilvers Member Posts: 182
If I follow the Pumping Away layout, which calls for only one purge, should I not put drains in other locations - such as above and below the circulator, or above the ZWs? Does adding more ruin the purity of the design?
  • STEVEusaPA
    How many zones, how is it piped, zone valves or circulators, what type of emitters?
    In general you can put in as many as you want, but with a proper 'pumping away' with that valve in the right spot and oriented correctly, and the fill in the right spot, should be all you need.
    I like isolating the circulators, for easy replacement, but with a micro reabsorber air elimination, no purge needed on them.
  • rsilvers
    Six zones.
    It will be repiped.
    Zone Valves and one circulator.
    Circulator will have flanges with shutoffs built in.
    Can the micro bubble work with antifreeze and not clog?
  • SuperTech
    SuperTech Member Posts: 2,669
    Yes the microbubble resorber can work with antifreeze but don't use antifreeze unless it's absolutely necessary.  Antifreeze requires annual checking and it will need replacement when it becomes corrosive.
  • Zman
    Zman Member Posts: 7,614
    Pumping away and drains/purge points are not really related. Put drains and purge points where you need them in order to service the system.
    Albert Einstein