steam in wet return

tseghaye
tseghaye Member Posts: 2
Why my wet return acts as steam supply ?

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 24,876
    Two reasons come to mind right away -- a failed trap or traps or, more likely the boiler was replaced and the new water line is lower than the old one was.

    Could also be much too high pressure and poor near boiler piping (no equalizer)
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • tseghaye
    tseghaye Member Posts: 2
    how high should the water line be from the floor. by the way the boiler is an old McLain steam boiler
  • JUGHNE
    JUGHNE Member Posts: 11,279
    Show us pictures of boiler and floor to ceiling piping.
    Include the wet return for reference in regard to the sight glass.
  • Jamie Hall
    Jamie Hall Member Posts: 24,876
    tseghaye said:

    how high should the water line be from the floor. by the way the boiler is an old McLain steam boiler

    There is no exact figure. Far more important is how low should the wet returns be? And the answer to that is they should nowhere be less than six inches below the boiler water line. Check out in the wilderness --- they sometimes rise up rather staying on or near the floor where they belong.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England