Air Pressure Test
1887House
Member Posts: 3
Greetings:
I'm adding a radiator circuit to my system. It's 1/2 inch PEX feeding 3 cast iron baseboards. There are 6 ground joint unions attaching the radiators. When I pressured the circuit up to 30 PSI, it dropped 2-3 pounds over 4 days. I am assuming ZERO drop is the result I'm looking for. I have ball valves I close after pressurization. Any helpful hints would be greatly appreciated. Do I need to hose down the unions with leak detector bubbles?
I'm adding a radiator circuit to my system. It's 1/2 inch PEX feeding 3 cast iron baseboards. There are 6 ground joint unions attaching the radiators. When I pressured the circuit up to 30 PSI, it dropped 2-3 pounds over 4 days. I am assuming ZERO drop is the result I'm looking for. I have ball valves I close after pressurization. Any helpful hints would be greatly appreciated. Do I need to hose down the unions with leak detector bubbles?
0
Comments
-
Air tests are very unreliable (as well as dangerous). Now that you have done that, though, and find you have no catastrophic leaks, do it again with water. Pressurize it to 20 psi or so, close it off from the rest of the system, and watch it for an hour or two. No drop? Good to go.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Yeah, put water to it. the air test proved there are probably no big leaks0
-
Not full house pressure, as said 20 PSI is plenty.
Your boiler relief valve will only allow 30 max.....20 may be normal operating pressure.
It is just that water is thicker than air and probably not leak after your first test results.0 -
You could leave the air for a couple days and see if it continues to fall. It can vary a bit with temp but if it keeps falling and never goes back up it is a leak. I had a really tiny leak in a propex fitting that I saw a very slow decrease in air pressure but I was able to see a bead of water once I added water to the system(I used a funnel and a bucket then used air to pressurize it, not the ideal method).0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements