GB 142 gurus...
kcopp
kcopp Member Posts: 4,630
I have a low/ no heat call to go to in the morning.
Customer says there are getting error codes of OY, 2F and 4F..
Im looking all over... could be air bound or bad sensors.
Any thoughts so i can get a head start of making a repair?
TY, kevin
  • https://www.powerequipmentdirect.com/manuals/GB142Service.pdf
    See p. 22 for "OY" (also a Jewish term for when you're in trouble) and page 23 for "2F". I don't see anything for 4F.
    kcopp
  • kcopp
    Thanks.
    makes me think more so that this unit is air bound...
  • Ironman
    Ironman Member Posts: 7,857
    All those codes are dealing with the supply temp being too high: flow problem or bad sensor.
    Bob Boan
  • kcopp
    Turns out it was air bound. Someone had closed the little cap on top of the integrated air vent. Opened up the cap air vented out and it fired right up. The sensors were doing their job... boiler was overheating.
    Brent H.Ironman