Steam System Nomenclature
stormbytes
stormbytes Member Posts: 36
edited January 2022 in THE MAIN WALL
Please explain the following terms:
1. Runouts
2. Take-offs
3. Risers
4. Drips
Feel free to add more anatomy if I left any out :)
Tia!
PS: Already bought / reading Dan’s book.
    EBEBRATT-Ed Member Posts: 19,458
    Runout a pipe feeding or returning from a radiator consisting of horizontal and vertical pipe
    Take off a run out's or branch pipe connection to supply or return main
    Risers a vertical pipe could be supply or return with flow up or down
    Drips a pipe dripping (draining) condensate from a steam pipe either from a main, riser or runout
    or branch
    Steam branchor a pipe with a take off from a steam supply or return main that feeds several takeoffs
    return branch
    Some might call a branch a sub main
  • stormbytes
    @EBEBRATT-Ed
    Thanks for that info!
    What's the difference between a runout and a takeoff ?
  • ratio
    ratio Member Posts: 4,175
    The runout starts at a takeoff.
  • stormbytes
    @ratio
    What do you call a pipe that leaves the main and connects to a radiator? Its as if its both?
  • ratio
    The takeoff is where the runout attaches to the main.