HX for Steam to Water

kcopp
kcopp Member Posts: 4,462
Hi All.
I have a system out there that i have inherited to care for.
Peerless 63 series steamer w/ a hot water loop off the side.
Brazed plate HX to feed the system off the condensate. Overall installed well.
here's the issue.... After2-3 months of running in season the customer complains that the baseboard is not getting warm enough. I run over and the BPHX is mucked up.
I flush it out and all is fine...until it happens again.
I have flushed out the steam side and didnt make much difference.
Thoughts?
Is there a more robust HX to use?

TY, kevin


Comments

  • EzzyT
    EzzyT Member Posts: 1,337
    Checkout Everhot copper shell in tube hx. I’ve installed a ton of them and they work perfectly.
    E-Travis Mechanical LLC
    Etravismechanical@gmail.com
    201-887-8856
    kcoppSTEVEusaPAmattmia2STEAM DOCTOR
  • kcopp
    kcopp Member Posts: 4,462
    Thanks much!
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,222
    @kcopp

    Are you pumping the steam side or is it gravity?
  • kcopp
    kcopp Member Posts: 4,462

    @kcopp

    Are you pumping the steam side or is it gravity?

    Pumped
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,222
    @kcopp

    I am assuming that @EzzyT is reffering to the Everhot "external tankless water heater". Those certainly should not plug as fast as a plate & frame.

    I assume you are coming out of the boiler just below the water line and pumping back in down low to keep head on the pump with the pump on the lower connection
  • mattmia2
    mattmia2 Member Posts: 10,655
    edited January 2022
    Or other shell and tube hx

    Or put a tankless coil in the boiler as a hx if one is available and the plate on the boiler looks like it would come off.
  • kcopp
    kcopp Member Posts: 4,462

    @kcopp

    I am assuming that @EzzyT is reffering to the Everhot "external tankless water heater". Those certainly should not plug as fast as a plate & frame.

    I assume you are coming out of the boiler just below the water line and pumping back in down low to keep head on the pump with the pump on the lower connection

    correct
  • STEAM DOCTOR
    STEAM DOCTOR Member Posts: 2,143
    The plate HX has very small passageways. Very susceptible to clogging. 
    kcopp
  • ethicalpaul
    ethicalpaul Member Posts: 6,286
    I have a water loop on my 63 with no issues so far (although I'm pumping directly from the boiler to the loop, no exchanger) so I have some questions for you:

    Which port on the boiler are you pumping from? What is the PH of the boiler water?

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el