I have a system out there that i have inherited to care for.
Peerless 63 series steamer w/ a hot water loop off the side.
Brazed plate HX to feed the system off the condensate. Overall installed well.
here's the issue.... After2-3 months of running in season the customer complains that the baseboard is not getting warm enough. I run over and the BPHX is mucked up.
I flush it out and all is fine...until it happens again.
I have flushed out the steam side and didnt make much difference.
Thoughts?
Is there a more robust HX to use?
TY, kevin
  • EzzyT
    EzzyT Member Posts: 1,380
    Checkout Everhot copper shell in tube hx. I’ve installed a ton of them and they work perfectly.
    E-Travis Mechanical LLC
    Etravismechanical@gmail.com
    201-887-8856
    kcoppSTEVEusaPAmattmia2STEAM DOCTOR
  • kcopp
    Thanks much!
    EBEBRATT-Ed Member Posts: 20,397
    @kcopp
    Are you pumping the steam side or is it gravity?
  • kcopp
    @kcopp
    Pumped
    @kcopp
    I am assuming that @EzzyT is reffering to the Everhot "external tankless water heater". Those certainly should not plug as fast as a plate & frame.
    I assume you are coming out of the boiler just below the water line and pumping back in down low to keep head on the pump with the pump on the lower connection
    mattmia2 Member Posts: 17,221
    edited January 2022
    Or other shell and tube hx
    Or put a tankless coil in the boiler as a hx if one is available and the plate on the boiler looks like it would come off.
  • kcopp
    @kcopp
    correct
  • STEAM DOCTOR
    STEAM DOCTOR Member Posts: 2,617
    The plate HX has very small passageways. Very susceptible to clogging.
    kcopp
    ethicalpaul Member Posts: 8,925
    I have a water loop on my 63 with no issues so far (although I'm pumping directly from the boiler to the loop, no exchanger) so I have some questions for you: