I woke up one morning to a cold house (temp was at 58*, thermostat set at 65* and calling for heat). I had just serviced it back in the beginning of October with new filters, nozzle, etc. to which it has been running fine since. My low water cutoff is working as it should, and the switch opens and closes as it should. I have blew threw the pigtails making sure they are clear. I have replaced the oil primary control, the fan center switch and transformer. The oil primary reads that the Limit Circuit is OPEN. If i jump the R and G terminals on the fan center switch, the limit closes and allows the unit to fire. At this point, i am leaning towards a bad Pressuretrol or something is wrong with my Cyclegard CG450. Is there anyway to bypass these, or further test them without replacing them?
0
Comments
-
0 -
If you jump R & G and it fires the limits are ok......that's what it should do.
It's not a limit. Sounds like your thermostat is not pulling in the fan center. Take the thermostat apart and jumo W & R and see if it fires.
Thermostat batteries dead?0 -
Oil limit controls must be wired 120V, not 24V. You don't need that fan centerTo learn more about this professional, click here to visit their ad in Find A Contractor.0
-
Burnham and other makers supply that fan center to get around the fact that Riello burners don't have thermostat terminals. This one has a Beckett but I'd bet the TT terminals on the primary are jumped from the factory.Robert O'Brien said:Oil limit controls must be wired 120V, not 24V. You don't need that fan center
The limit controls are supposed to be wired into the 120V circuit before it gets to the relay contacts. For whatever reason, someone has added redundant limits to this boiler and wired them into the 24V circuit. Maybe the inspector wanted them?
I'd make sure the #67 low-water cutoff and the Pressuretrol mounted above it are working properly.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
EBEBRATT-Ed said:If you jump R & G and it fires the limits are ok......that's what it should do. It's not a limit. Sounds like your thermostat is not pulling in the fan center. Take the thermostat apart and jumo W & R and see if it fires. Thermostat batteries dead?
Robert O'Brien said:Oil limit controls must be wired 120V, not 24V. You don't need that fan center
Steamhead said:Oil limit controls must be wired 120V, not 24V. You don't need that fan center
Burnham and other makers supply that fan center to get around the fact that Riello burners don't have thermostat terminals. This one has a Beckett but I'd bet the TT terminals on the primary are jumped from the factory. The limit controls are supposed to be wired into the 120V circuit before it gets to the relay contacts. For whatever reason, someone has added redundant limits to this boiler and wired them into the 24V circuit. Maybe the inspector wanted them? I'd make sure the #67 low-water cutoff and the Pressuretrol mounted above it are working properly.0 -
Turn off the power, disconnect the wires in the Pressuretrol and use your ohmmeter to make sure there is continuity between the screw terminals.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
You have to get a test meter and trace the circuit out and figure what is open. If you jumped R &G and the burner fires look at whats wired in to R & G
Probably the pressure control and/or low water cutoff. Check the pressure control as @Steamhead mentioned. The ones mounted on the low water cutoffs tend to plug the pig tail and your pigtail looks like it's a steel, brass is much better0 -
Should work..............All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
@ktm1217
Take the wires off the pressure control mounted on the low water cutoff and ohm out the control itself. Could be 0 ohms or have continuity. Also do that to the low water cutoff (top two terminals) put wires back when done
0 -
EBEBRATT-Ed said:@ktm1217 Take the wires off the pressure control mounted on the low water cutoff and ohm out the control itself. Could be 0 ohms or have continuity. Also do that to the low water cutoff (top two terminals) put wires back when done0
-
Update: after some hunting, it was discovered that the thermostat wiring had disconnected at a splice (I believe i may have hit it when stacking firewood in my basement). All is working now!
However, we did find that my Cyclegard CG450 was hooked up wrong by someone previously and wasnt allowing the burner circuit to cut out for low water. Since fixing that connection, i found that the boiler cuts off every 10-15mins when running for the system to do a ILT. I think I may switch that cyclegard out for a safgard over the summer.
Thank you everyone for the help! Kinda cant believe i didnt find that disconnected connection, but glad its up and running!0 -
You just dodged a bullet. If the boiler had gotten low on water and the low-water cutoff had failed to stop the burner, you would have had a cracked boiler. The last thing you need in the middle of winter is to have to replace your boiler.
Did the other low-water cutoff work as designed?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Steamhead said:You just dodged a bullet. If the boiler had gotten low on water and the low-water cutoff had failed to stop the burner, you would have had a cracked boiler. The last thing you need in the middle of winter is to have to replace your boiler. Did the other low-water cutoff work as designed?
0 -
So you got the cyclegard wired up correctly by a licensed steam pro (or by someone who really knows their stuff)? That would be good.
The cyclegard's interruption is not bad at all, I think it is the safest LWCO out there. Run it this season and see if you can get used to it doing its job. I really like mine now after having lived with it.
Also I don't think you are measuring the resistance of the controls correctly. In its normal state the pressuretrol should be absolutely zero ohms with no other reading possible. It's basically a piece of wire when it's not in the "cut out" state. Same for the LWCO. But that's OK it looks like you found the problem.NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements