Baseboard to towel heater radiator conversion, how many BTU/hr?

vilord
Member Posts: 48
Hi there!
I'm sure a similar question has been asked before, but a quick search didn't really give me the answer I was seeking. Hopefully this is a quick one.
We're renovating our bathroom, which currently has two fin tube baseboard convectors with a total 7'6". They're 'heatrim american' which is rated at about 580 BTU/hr per foot at 180 degree water temp. We actually run 130-150 degree water, but the towel heaters are all rated with 180 water.
I'd like to replace the 3'6" portion, so I think I want a towel heater with about 2000 BTU/hr rating with 180 degree water. Am I doing the math right, or is there more to it because I'm switching from a convector to a radiator? I'm hoping to pick out and get the towel heater ordered so it's here when the plumber arrives.
Thanks all!
Jesse in Massachusetts
I'm sure a similar question has been asked before, but a quick search didn't really give me the answer I was seeking. Hopefully this is a quick one.
We're renovating our bathroom, which currently has two fin tube baseboard convectors with a total 7'6". They're 'heatrim american' which is rated at about 580 BTU/hr per foot at 180 degree water temp. We actually run 130-150 degree water, but the towel heaters are all rated with 180 water.
I'd like to replace the 3'6" portion, so I think I want a towel heater with about 2000 BTU/hr rating with 180 degree water. Am I doing the math right, or is there more to it because I'm switching from a convector to a radiator? I'm hoping to pick out and get the towel heater ordered so it's here when the plumber arrives.
Thanks all!
Jesse in Massachusetts
0
Comments
Categories
- All Categories
- 86.9K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 57 Biomass
- 425 Carbon Monoxide Awareness
- 109 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.7K Gas Heating
- 105 Geothermal
- 160 Indoor-Air Quality
- 3.6K Oil Heating
- 70 Pipe Deterioration
- 972 Plumbing
- 6.3K Radiant Heating
- 386 Solar
- 15.4K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 44 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements