Dunkirk 90 Quantum

Options
Johny86
Johny86 Member Posts: 3
Hello guys i have Dunkirk 90 Quantum.  When my zone 2 is trying to turn on its making clicking noise and seems like it can not connect to turn it on.  

Please any help is appreciated.

Comments

  • Johny86
    Johny86 Member Posts: 3
    Options
    If you copy the link i posted video on Youtube.
    Thank You
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,540
    Options
    I assume you have 2 zones? I would try bypassing the thermostat connections in the Taco panel mounted on the wall. Check batteries in your thermostat if they have batteries
  • Johny86
    Johny86 Member Posts: 3
    Options
    Yea 2 zones.
    did all that and it still keep doing same thing.  Dose not want to connect just keeps clicking.
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,540
    Options
    Would like to help but you really need someone with a test meter and the boiler wiring diagram to track this down. Could be a loose wire or a bad control
    Ironman
  • Ironman
    Ironman Member Posts: 7,376
    Options
    You could try temporarily jumping the “end switch” terminals in the Taco panel. If that causes the boiler to operate, then the problem is with the Taco or a thermostat. If not, the problem is in the boiler.

    Have you checked the condensate trap and drain for blockage? 