Is it normal for the pressuretrol not to trigger?
zx2slow
Member Posts: 1
Long time lurker here, trying to sort out if my boiler is working properly. My concern is that I have been monitoring my new boiler pretty closely and it seems to only shut off when the thermostat hits the set temp, I have never noticed the pressuretrol shutting off the boiler. My setback is only around 4-6F normally, the house generally gets up to temp in about 45min. I'm in New Hampshire and the weather has been fairly mild, should I expect to see the pressuretrol cut the boiler once it gets very cold?
Some background:
I have just had a new Burnham IN6 installed to replace an older IN6 that failed after corrosion rotted a hole in the block. I replaced all the radiator vents with ventrite #1's and the mains with Gorton #2's and all appear to be venting and sealing properly. When the boiler cuts off I can hear some of the vents opening and sucking in air.
The new pressuretrol that was included with the boiler is set to the minimum of 1.5psi with a .5 psi differential along with a near useless 30psi gauge - I'm blind as to what the actual pressure is. I understand that at minimum settings these are pretty inaccurate. I plan to purchase a 3 or 5 psi guage and install it on a T off the pigtail the pressuretrol is on and eventually a vaporstat.
Some background:
I have just had a new Burnham IN6 installed to replace an older IN6 that failed after corrosion rotted a hole in the block. I replaced all the radiator vents with ventrite #1's and the mains with Gorton #2's and all appear to be venting and sealing properly. When the boiler cuts off I can hear some of the vents opening and sucking in air.
The new pressuretrol that was included with the boiler is set to the minimum of 1.5psi with a .5 psi differential along with a near useless 30psi gauge - I'm blind as to what the actual pressure is. I understand that at minimum settings these are pretty inaccurate. I plan to purchase a 3 or 5 psi guage and install it on a T off the pigtail the pressuretrol is on and eventually a vaporstat.
0
Comments
-
If the boiler is size right you can usually operate on the thermostat and never see pressure on the gauge.
Since this is a new boiler I assume the pigtail can't be plugged (maybe a bad assumption)
Take the cover off the pressure control and trip the pressure control with a screwdriver with the burner running
And post some pictures of the boiler and the piping0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements