Hi, my boiler for last few days have been having issues starting up. I thought it was a bad thermostat so i changed, same issue.
When thermostat calls for heat, it makes click sound, i check basement boiler. Burners not on. Pilot is on, I noticed damper opened. LWCO is green, plenty of water. Damper stayed open entire time since thermostat called for heat. If i power off thermostat then on or lower temp and bring up it will go on and flames come on. This happens sporadically.
PSEG was here two weeks ago, he cleaned out dirty water and did lower output a little.
Im Stumped

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 23,367
    Options
    Ah -- has this been happening more or less since PSEG was there? I'd get them back...

    If they can't fix it, then you'll need someone with the necessary measuring devices -- and the skill to use them to troubleshoot this. There are a number of things which could be amiss.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • sonicboomin
    sonicboomin Member Posts: 11
    Options
    Pseg was here 2 weeks ago. This started 3 days ago. They scheduled to come again tomorrow 
  • JUGHNE
    JUGHNE Member Posts: 11,069
    Options
    Is this a standing pilot or is it ignited with each call for heat?
  • sonicboomin
    sonicboomin Member Posts: 11
    Options
    Standing pilot
  • JUGHNE
    JUGHNE Member Posts: 11,069
    Options
    The tstat opens the vent damper, when it is in the open position (the shaft is parallel to the flue pipe) there is a small end switch that sends power to the gas valve.

    When the damper is open, look for a small switch on the motor that states "manual open" or something to that effect.
    That should close the end switch for firing the boiler.
    The damper must stay open full time for the boiler to light.

    You may need a new damper motor, the end switch may be hit and miss as far as closing when it should.
  • sonicboomin
    sonicboomin Member Posts: 11
    Options
    Thanks all. Yes and I noticed the damper was open however burners were not firing that is the issue. 
  • Erin Holohan Haskell
    Erin Holohan Haskell Member, Moderator, Administrator Posts: 2,313
    Options
    @sonicboomin, I've combined your two posts into one here. Thanks!

    President
    HeatingHelp.com

    sonicboomin
  • neilc
    neilc Member Posts: 2,705
    Options
    #pigtail

    go bang on your Ptrol,
    and post a picture of it and the pigtail,
    raise the setting one turn, temporarily

    pigtail is clogged?
    known to beat dead horses
  • JUGHNE
    JUGHNE Member Posts: 11,069
    Options
    If the ptrol was not closed there would be no call for heat and the vent damper would not open.

    Did the OP move the switch on vent damper to manual on and then get heat???
  • neilc
    neilc Member Posts: 2,705
    Options
    JUGHNE said:

    If the ptrol was not closed there would be no call for heat and the vent damper would not open.

    ok, good point,
    but things never get wired funny either, right?
    known to beat dead horses