YORK gas furnace, with WR/Emerson 50E47-070
wildmanwilly
Member Posts: 4
Having an intermittent lockout issue with this furnace, got to it today with the continuous flash lockout, reset it, flame sense was teetering .9-1.1ųA, assumed that was the problem as after I cleaned it, it returned to 3.3-3.4 range, but now 4 hours later it's back doing it again, but when I cycle it (previously cycled it 50+ times) it won't repeat, checked flame sense, grounding, xfmr voltage is good, 26.7-27.4, line voltage is 125v, checked neutral to ground with a load on the furnace for a bonding problem at panel, but only saw .2-.34v, any ideas? I'm stumped and can't get ahold of York tech support but don't wanna leave my customer without heat.
0
Comments
-
What code is the board flashing?Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
There are no codes on the board. As stated, it just has the continuous flash indicating lockout.0
-
-
Yes, I have, but this control will not lockout due to failed proving on either of the pressure switches, I thought that may be it as well.0
-
For anyone curious it was the 50E47, replaced it with a new 843, and it hasn't done it since the day after this post was made.0
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 927 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements