Gauges look alright?

nedsparrow
nedsparrow Member Posts: 6
a video of my boiler which is turning on only intermittently, not enough to heat the little house. Do the gauges look all right? If so, think I'll change fuel filter . Maybe find filter @ auto or farm store 

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 24,543
    The photo of the gauge is completely illegible, so I wouldn't care to say whether it's alright or not.

    What do you mean by turning on only intermittently? Presumably there is a thermostat? If so, what happens if you turn it way up? Anything?

    And what type of system is this? I'm guessing oil fired hot water, but could be oil fired air or...

    A little more information would be useful.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    nedsparrow
  • nedsparrow
    nedsparrow Member Posts: 6

  • nedsparrow
    nedsparrow Member Posts: 6
    Oil-fired hot water system. Red manual override light was on and red button finally reset and now it's burning great… Thanks for help
  • nedsparrow
    nedsparrow Member Posts: 6
    Circulating pump remains on but boiler shut off after eight minute burn. Temperature only got to 100°. Red reset button doesn't do anything now. Calling for more heat at the thermostat but not coming  up. Now where can I get a new oil filter?
  • nedsparrow
    nedsparrow Member Posts: 6

  • nedsparrow
    nedsparrow Member Posts: 6
    Now up to 122 @ boiler from that same burn. Circulator pump is still running but radiators are cold upstairs
  • KC_Jones
    KC_Jones Member Posts: 5,800
    Do not keep hitting the reset.  There is a problem and it needs to be serviced/repaired.

    When was the last time you had the burner serviced, cleaned, and set up with a combustion analyzer?
    2014 Weil Mclain EG-40
    EcoSteam ES-20 Advanced Boiler Control
    Boiler pictures updated 2/21/15
    nedsparrowHVACNUTEBEBRATT-Ed
  • STEVEusaPA
    STEVEusaPA Member Posts: 6,505
    You really need a professional to come in there and make it right. Just changing the filter, that you CAN'T find at a auto parts store isn't going to help.

    There was an error rendering this rich post.

    HVACNUTEBEBRATT-Ed
  • Jamie Hall
    Jamie Hall Member Posts: 24,543
    By what logic is changing an oil filter going to change an overheating problem?

    As @STEVEusaPA and @KC_Jones have said, do NOT keep hitting the reset button. Even once, without knowing what the problem is, is one time to many. Many times is likely to result in blowing up the house.

    Turn the thing off with the emergency switch and get a tech. in there who can find and fix the problem.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    EBEBRATT-Ed
  • HVACNUT
    HVACNUT Member Posts: 6,234
    Oil-fired hot water system. Red manual override light was on and red button finally reset and now it's burning great… Thanks for help
    That's a scary quote.

    Please stop touching it and find a reputable oil tech.

    Even if you were able to replace the oil filter, you wouldn't be able to get it started because you introduced air into the oil line and the air must be bled out. 
    Save the aggravation. 

    When you make the calls, ensure the tech has a combustion analyzer and will leave or email a copy of the report. 

    Looks like an American Standard Arcoliner and if the gauge is correct, then the expansion tank must be drained as well, and the pressure reducing valve tested.
    Without service, the relief valve will soon blow, if that works.
    EBEBRATT-Ed