Adding main vents where there none atm
mygardenshed
Member Posts: 51
Our new heater is up and running fine. Install thread here: https://forum.heatinghelp.com/discussion/185857/new-steam-boiler-install#latest
I’m now in the process of getting it balanced. The only vent at the moment is on the condensate return. There was a Hoffman No. 4 that was shot so I bought a Gorton #2. It was too big for the current vent so I returned it and bought a Dole No. 4 which is basically a Hoffman but has 3 vent holes as opposed to the Hoffman’s 1. Seems to be venting just fine.
My question is:
There are currently no vents and the ends of the mains. Should I try to install one if I can?
The one main has a tee and a 90° for the final radiator takeoff. Would it be beneficial to change the 90° to a tee and install a vent there. The other main is behind a finished wall and I’m not too thrilled about tearing into it there would be no benefit.
Some photos:
After the radiator takeoff the main drops down into the wet return .
I’m now in the process of getting it balanced. The only vent at the moment is on the condensate return. There was a Hoffman No. 4 that was shot so I bought a Gorton #2. It was too big for the current vent so I returned it and bought a Dole No. 4 which is basically a Hoffman but has 3 vent holes as opposed to the Hoffman’s 1. Seems to be venting just fine.
My question is:
There are currently no vents and the ends of the mains. Should I try to install one if I can?
The one main has a tee and a 90° for the final radiator takeoff. Would it be beneficial to change the 90° to a tee and install a vent there. The other main is behind a finished wall and I’m not too thrilled about tearing into it there would be no benefit.
Some photos:
After the radiator takeoff the main drops down into the wet return .
0
Comments
-
The idea of a T where you have circled and adding a vent there is a good idea. However. Unless there is a handy union somewhere nearby, it could be a real job...Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Where is that Dole #4 installed on the system? Post a pic. Also, is this a one-pipe or two-pipe system?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
There is a union on the radiator piping. As you can see there’s not enough room for a very large vent.Jamie Hall said:The idea of a T where you have circled and adding a vent there is a good idea. However. Unless there is a handy union somewhere nearby, it could be a real job...
0 -
Two pipe system. Seems to be running at a nice pressure.Steamhead said:Where is that Dole #4 installed on the system? Post a pic. Also, is this a one-pipe or two-pipe system?
The other day I went through the radiators one by one, system off of course, and removed each trap cage and cleaned the trap base. While the cages were out I gave them a good wipe down and heated them up with a heat gun and made sure they were opening and closing. Also while the trap was open I sent a shot of compressed air down the condensate line via the port at the base of the trap to be sure there are no obstructions.
Discovered one trap that’s suspicious. I think it’s in the pipe leading from the trap and into the return. Replacing the piping shouldn’t be too bad as it’s exposed in the basement.
0 -
Follow up question is if I install a vent at the location discussed above and not install one at the end of the other main will this lead to an imbalance? I’m thinking yes.
I may install one and if it creates trouble due to an imbalance I can always put a pipe plug in it’s place.
Thanks0 -
When I discovered I had no main vents a few years back, I installed the biggest vents I could find on the last radiator on each branch as an interim measure. A "D" radiator vent is as fast as a #1 main vent. Unless that radiator happens to be right next to your thermostat, you might give that a try.Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-240
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements