Quick question re. the 24" rule
Hap_Hazzard
Member Posts: 2,846
TLAOSH and other sources say to allow at least 24" from the water line to the bottom of the header, but what about drop headers? Would the bottom of the swing-arm be a good point of reference in that case?
Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-24
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-24
0
Comments
-
Basically. seems to me anyway. I seem to recall from some discussions years ago that the idea was to have enough height to allow entrained water droplets to slow down, get todther, and fall back, and I also seem to recall that it was a rule of thumb kind of thing.
Cedic's drop header is all of about 8 inches above the boiler water line -- as low as Charles could get it without hitting the block! -- and it works fine.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
Yes. The critical dimension is how high the riser from the boiler goes. That's why Cedric's header works so well.Hap_Hazzard said:TLAOSH and other sources say to allow at least 24" from the water line to the bottom of the header, but what about drop headers? Would the bottom of the swing-arm be a good point of reference in that case?
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting1 -
You just can't put the drop header below the boiler water line0
-
You kid, but I wouldn't bet that no one has ever tried it.Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-240 -
@Hap_Hazzard if the equalizer goes back into the boiler and you put a drop header below or at the water line the water line in the header will match the height in the water gauge glass on the boiler.0
-
I have seen drop headers go below the water line where the boiler was installed in a low crawl space or low ceiling basement.
At the low end of the drop header a condensate drain line was installed with a steam trap. the discharge of the steam trap was piped to a condensate pump.Steam: The Perfect Fluid for Heating and Some of the Problems
by Jacob (Jake) Myron0 -
@dopey27177
yes with a steam trap piped to a condensate or boiler feed pump the header can be anywhere. But with an equalizer going back to the boiler you have to have the bottom of the header above the boiler water line +28"/lb of steam pressure.+ a few " as as margin for error.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements