orifices
skaterrobb
Member Posts: 7
I've been trying to do the math can't get it or figure out what kind of lp orifice size I need
No one in my area professionaly seems to know anything
This is the info found on the sticker inside
I'm just trying to keep my kids warm
Model: M7TL 045A BW
Serial: M7G161212741
0-4999ft(1524m) above sea level
Max input 45000btuh/29000btuh
Out put 42750btuh/27550btuh
Gas supply pressure
Max 13.0
Min 11.0
Manifold 10.0
External static pressure 0.3
Where I live 298ft above sea level
Please and thank you
0
Comments
-
Is this a Miller/Nordyne furnace? One would think if you called the manufacturer they'd be able to provide the proper part number.
Where are you located?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting1 -
When a furnace runs on LP gas the gas pressure on the OUTLET side of the gas valve should be 10" of water column. The LP INLET pressure to the gas valve should be 11-13" water column.
The correct size orifices should be installed (or should have been installed) when start up was done
As far as I know, most all furnaces are shipped with natural gas orifices and the propane orifices and maybe a new spring for the gas valve must be installed before start up.
I looked on line for the manual and it didn't come up but I didn't look that hard.
If you have the manual it should list the orifices for natural gas or propane.
Is this a new install or existing? What problem are you having?0 -
The Original furnace died and a neighbor gave us the one I'm asking aboutya I've been looking for the manual for 2 yrs and never came with oneWhere the flames are that compartment gets to hot and sets off the safety switch3 orifices the last one the blue flame won't contain it's self into the burner tubeThere other 2 orifice are size 60 and 59 but the last guy we had look at drilled them so I don't even know what size they really are the orifice not working is a 55 but drilledFrom what I can put together a #56 0.56mm should workJust trying to provide what info I do have0
-
-
I've tryed finding professional 3 of them just said I dk 1 did something couldn't explain thoughabd our provider Johnson and Johnson I knew more then the guy they sent out Ive been fighting with this furnace for 2 years trust me I'm to the point I would be happy just to find a pro that would know somethingI'm located upstate Oswego NY0
-
0 -
Your first post mentioned LP gas. If your on LP those orifices could be too large. It tells you right on the nameplate "FACTORY EQUIPPED WITH #49 ORIFICES FOR NATURAL GAS"
What are you burning?
The manual is attached. Go to Nortek global and search "technical literature"
Call Nortek at 800-422-4328
They can tell you where to get parts and maybe find you a contractor0 -
The correct orifice size and gas pressure for propane are detailed in Table 11 in the manual depending on your height above sea level0
-
Burning propaneIve stuck half of my body inside looking for the manual can't find one online but I will use that number if I could I would switch to natural gas but for some reason can'tI have looked up tables but I'm so unsure of my measurements I understand how risky this **** is I'm not having fun lol0
-
This furnace is designed for use in manufactured housing. Here is the technical infor for your furnace.
http://literature.nortekhvac.com/pdf/182C565B-0C08-D5E9-C243-66E87605D317&clientkey=4CCCED29-5ABE-42D8-B8E3-3AE0DBB2B8B9
Your I/O manual is here
https://www.manualslib.com/manual/1110649/Intertherm-M7rl-Series.html?page=23#manual
And your orifice sizes need to be looked up on a chart like this one
https://ssl.ca/wp-content/themes/sinclair-supply/pdf/Gas-Orifice-Capacity-Chart.pdf
That furnace should have a gas valve with a two position regulator. you need to set the regulator in the gas valve to NAT or LP based on the type of gas you are connected to.
The correct drill size orifice for LP is a 29
The correct drill size orifice for Natural gas is a 46
In order to know what drill have, since the orifices you have may have been drilled out, is to get a machinist numbered drill set. ...OR... purchase the correct size orifice from Nordyne or a supply house that sells Nordyne parts.
Combustion test is difficult on this furnace because there is no place to drill in the vent pipe for combustion testing. the vent connector is inside a concentric inlet pipe attached to the top of the furnace. You just got to go with the factory settings in many cases. I have on occasions places a 3/8" copper tube thru both pipes in order to get a combustion reading on a problem job. but for the most part, you just set it and look at the flame thru the sight door, to see if it is blue.
The LP company or the Natural gas company will have a really old service tech that knows how to set them up. If not change LP companies. If natural Gas supplier does not have a experienced tech then I don't know what to tell you.
Hope this helps.
Mr.Ed
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
2 -
@skaterrobb
I don't know what more we can do. I posted the entire manual attached to my post above. You asked about orifices and gas pressures for propane it's all in the manual. All you need to know is you city height above sea level to select the correct orifice. All the information to start and adjust the furnace is in the manual
Your really going to need some technical help. I suggest you call Nortek tomorrow. I am sure someone in your area is a Nortek dealer that they can point you to. Have then give you a few names.
If you strike out go to a local heating supply house if you can find one that sells Nortek even better and have them make a few suggestions on who can service the furnace.
You need this fixed and a combustion test done1 -
I just was reading the manual and realized that this is a 2 stage condensing furnace. I wonder if the thermostat is connected to stage one or stage two? Do you have a 2 stage thermostat? if you have a one stage thermostat you can connected to stage one and two in order to get full capacity. 45,000 is not very big and if you are only firing on stage one then you won't get much heat out of it. check the thermostat wiring! you may need to add a jumper or remove a jumper
This is on page 22 of the manual
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
The OP stated that he’s 298’ above sea level. According to the I/O manual that Ed posted, 1.1mm orifices should be installed and the manifold pressure should be 4.2” on low fire and 10” on high fire.
@skaterrobb
Find a gas tech that can take this info, get the correct LP conversion kit and set it up right. No drilling out orifices.
This is very simple procedure for a competent tech.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
Beside all of the Orifice and gas pressure/ combustion test and adjustment one should not turn a Blind eye to the Blower speed setpoint which can affect the delta Tee between the supply and return column
Wrong Blower speeds can also affect the combustion and can have negative affects on the HX.0 -
@Derheatmeister I have been trying to figure that out to one guy set the fan on high and it was like a tornado in my place 😑 wish I knew how to read the table I understand the 1 on 0 off just where do I find the numbers I need
0 -
@EdTheHeaterMan yes I do have a second stage stat and the peg on the mother board is set to 2 stageI did see the link everyone is leaving thank you and I am using the info ordered some partsI have been using repairclinic.comWebsite could be better but I've never had a problem with them0
-
skaterrobb said:
@Derheatmeister I have been trying to figure that out to one guy set the fan on high and it was like a tornado in my place 😑 wish I knew how to read the table I understand the 1 on 0 off just where do I find the numbers I need
As you can see from the Name plate the temperature Rise is from 30F to 60F and the max temp is at 160F on the supply column...IT May be time to drill holes in the supply and returm duct work ,check the delta tee (Temperature difference between the columns) and adjust the speed accordingly...You can use a regular pocket type thermometer for this!
And as allways..... Make sure you have a good unexpired Carbon monoxide detectors installed in the house !!
Better safe that sorry..
0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements