Header Piping
denick
Member Posts: 10
I'm installing a new boiler and there is a 2 1/2" riser on the new boiler. The existing header is 4". The mains coming out of the header are 2".
Questions,
Can I increase the riser to 3" at the boiler nipple?
Make the drop into the header with 3"?
Keep the 4" header ?
Do the 4" to 2" T's in the header to the mains cause any increase in steam velocity?
Questions,
Can I increase the riser to 3" at the boiler nipple?
Make the drop into the header with 3"?
Keep the 4" header ?
Do the 4" to 2" T's in the header to the mains cause any increase in steam velocity?
0
Comments
-
Yes. Yes. Yes. Yes. Make sure (it's pretty obvious!) that the two mains come off vertically up, or no more than 45 degrees off vertically up, from the header, and that they are after the boiler riser. Make sure that the reduction in size on the equalizer is on the vertical part after dropping from the header.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
As long as the take offs to the mains from the header are at least the size of the mains your fine. Ditto everything @Jamie Hall
In this case bigger is better. as long as you meet the MFG minimum you are fine if you exceed that your fine as well. Just follow the piping diagram0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements