Boiler autofill question
joe85
Member Posts: 2
Hi all,
I recently replaced a few items on my boiler (expansion tank, auto fill, pressure relief valve). It's been working good since, the boiler pressure is sitting right around 16-17 psi when hot which seems right for a large 2 story house (3000 sqft).
I checked the other day that my autofill was working and let some water out with the pressure relief valve and the autofill did not start introducing water back into the system until it was around 6 psi, which seems low. I know I can increase the psi with the adjustment screw on top of the autofill, will that cause the overall psi of the boiler to increase or will it just increase the psi at which the autofill kicks on?
Thank you!
I recently replaced a few items on my boiler (expansion tank, auto fill, pressure relief valve). It's been working good since, the boiler pressure is sitting right around 16-17 psi when hot which seems right for a large 2 story house (3000 sqft).
I checked the other day that my autofill was working and let some water out with the pressure relief valve and the autofill did not start introducing water back into the system until it was around 6 psi, which seems low. I know I can increase the psi with the adjustment screw on top of the autofill, will that cause the overall psi of the boiler to increase or will it just increase the psi at which the autofill kicks on?
Thank you!
0
Comments
-
That is a bit low. See if it comes back to where it belongs (you had it just about right!) and, if not, try the adjusting screw.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Jamie Hall said:That is a bit low. See if it comes back to where it belongs (you had it just about right!) and, if not, try the adjusting screw.0
-
Could've just been sticking. I always check pressure with my own gauge.
There was an error rendering this rich post.
0 -
@joe85
It might be possible that it was feeding at a low rate and you didn't think it was feeding. I wouldn't test it by popping the relief valve. They have a habit of leaking if you do that too much.
Also, do you have a backflow preventer. If so it should be upstream of the autofill. I have seen them put in downstream and they don't work that way0 -
Don’t everyone fire at me at once… my thoughts on PRESSURE REDUCING VALVES… valve it off. A building freeze is SIGNIFICANTLY cheaper and better off than a freeze with a flood on top of it. Trust me. I’ve seen the aftermath. If the boiler goes out your far better freezing and dealing with frozen burst pipes that at least can be dealt with in a controlled manner which is gonna suck absolutely- pressure reducing valve or “auto fill” valve=burst and water keeps on coming- flooding the building. I’ve seen icicles bursting through sheeting and siding. Trust me- your better off without it. That’s from experience and more than one personal eye witness accounts.1
-
Of course it will happen on a long weekend when no one’s around to catch it (commercial) or worse homeowner on vacation.0
-
I would say that most systems have a way of loosing pressure via packing glands or pex connections etc. Given that I would suggest against valving off as your chance of a frozen pipe is greatly increased when loss of pressure does not permit circulation. We don't shut the water off to our whole house everyday either.0
-
I would keep the pressure at 15 to 20 cold and 20 to 25 hot for a two story . And as long as it kicks back in and gets back to pressure within reasonable time I would not worry. Under 20psi hot seems low0
-
Have have you or anyone you know had an Autofill flood?
If you valve it off, why bother even installing one?
maybe a fill tank like an Axomin is a better choice. You have some reserve, and a very tiny flood potential
And the yearly backflow testing goes away, if an RPZ is requiredBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
hot_rod said:Have have you or anyone you know had an Autofill flood?
If you valve it off, why bother even installing one?
maybe a fill tank like an Axomin is a better choice. You have some reserve, and a very tiny flood potential
And the yearly backflow testing goes away, if an RPZ is required0 -
Fpipes said:I would say that most systems have a way of loosing pressure via packing glands or pex connections etc. Given that I would suggest against valving off as your chance of a frozen pipe is greatly increased when loss of pressure does not permit circulation. We don't shut the water off to our whole house everyday either.0
-
Kind of why up here with where we can and do see 30 below weather it’s recommended to leave a trickle of water at highest faucet especially with crawl spaces- the constant flow decreases chances of freezing.0
-
-
I had an Autofill flood a couple months ago. It was a fu*king mess. Luckily, I had a guest staying in a basement bedroom that alerted me to the water on the floor. It took a few minutes to figure out why the relief valve was pouring out water. The Bell & Gossett "Pressure Reducing Valve" was only about 10 years old. B&G stuff used to last 30-40 years. It think it all started with a dripping automatic air vent. So the Autofill was always working.hot_rod said:Have have you or anyone you know had an Autofill flood?
In the future, I'll shut the valve on the Autofill. I check the boiler often enough.
2
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements