zone valve control zvc403-4 wiring to boiler wont fire
oubegood
Member Posts: 5
good morning ,this is my first post and hope some one can save me . i think i have this wired right but it wont kick my boiler on . did i do some thing wrong or not
here are my pictures of the wiring can some one help me figure this out ?
here are my pictures of the wiring can some one help me figure this out ?
0
Comments
-
You boiler connection should be to the “isolated end switch” terminals next to the thermostat terminals, not the pump end switch terminals.
Also, make sure that your zone valve wires are in the proper order.
Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
thank you also are my zone valve wires messed up ?
0 -
-
heres my
tacos
0 -
all three in dependantly wired
0 -
Please post a pic that completely shows the zone panel.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
-
What was wrong?Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements