zone valve control zvc403-4 wiring to boiler wont fire

good morning ,this is my first post and hope some one can save me . i think i have this wired right but it wont kick my boiler on . did i do some thing wrong or not



here are my pictures of the wiring can some one help me figure this out ?

Comments

  • Ironman
    Ironman Member Posts: 7,537
    You boiler connection should be to the “isolated end switch” terminals next to the thermostat terminals, not the pump end switch terminals.

    Also, make sure that your zone valve wires are in the proper order.


    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
  • oubegood
    oubegood Member Posts: 5
    thank you also are my zone valve wires messed up ?
  • Ironman
    Ironman Member Posts: 7,537
    IDK. You haven’t shown what valves you have or how they’re wired.

    If they’re Taco 3wire valves, then follow the diagram. If they’re something different, then post some pics.
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
    oubegood
  • oubegood
    oubegood Member Posts: 5
    heres my

    tacos
  • oubegood
    oubegood Member Posts: 5
    all three in dependantly wired
  • Ironman
    Ironman Member Posts: 7,537
    Please post a pic that completely shows the zone panel.
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
  • oubegood
    oubegood Member Posts: 5
    got it all working perfectly thank you for the help your a awesome guy
    Ironman
  • Ironman
    Ironman Member Posts: 7,537
    What was wrong?
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.