Taco ZVC404 EXP - All valves open
stanleegoodspeed
Member Posts: 4
Hi all,
New homeowner here having an issue with my Taco Zone Relay. I have 3 zones. I recently replaced a thermostat (Honeywell non-progammable) in one of the zones, and now I'm having issues.
Currently, all valves are stuck open. The relay still recognizes all 3 thermostats when they call for heat (yellow light) but the valve open (red light) now only comes on for the upstairs thermostat. The two downstairs thermostats (including the new one I just replaced) do not trigger any valve functions. And I know all valves are stuck open because all the pipes get hot when the upstairs zone is triggered.
Any troubleshooting tips here? Can I manually reset the valves somehow?
Thanks!
New homeowner here having an issue with my Taco Zone Relay. I have 3 zones. I recently replaced a thermostat (Honeywell non-progammable) in one of the zones, and now I'm having issues.
Currently, all valves are stuck open. The relay still recognizes all 3 thermostats when they call for heat (yellow light) but the valve open (red light) now only comes on for the upstairs thermostat. The two downstairs thermostats (including the new one I just replaced) do not trigger any valve functions. And I know all valves are stuck open because all the pipes get hot when the upstairs zone is triggered.
Any troubleshooting tips here? Can I manually reset the valves somehow?
Thanks!
0
Comments
-
Some valves have a manual open lever. What valves do you have? Also What model thermostat was removed and what model thermostat was it replaced with? Posting a picture of the valve(s) may help.
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
Hi
if the only change was thermostat it could be a wiring issue. Remove the thermostat from RW terminals and see if board works normally.
if not remove all three stats and jump out RW terminals one zone at a time.My suspicion is your new stat is electronic and a resistor across W and C may be necessary try my diagnostic suggestion, and we’ll go to plan B if we have discovered issue.Also
you can contact Taco tech support for additional help.Those technicians love this stuff!
401-942-8000Joe Mattiello
N. E. Regional Manger, Commercial Products
Taco Comfort Solutions2 -
0
-
Were all three zones working correctly before you replaced the thermostat?
Is it possible there were issues when you purchased the house?
If so, is there $$ in escrow?0 -
@EBEBRATT-Ed No I'm trying to install a Honeywell CT87K1004 (Heat only).
@HVACNUT I'm actually not sure if this third zone was ever properly working. What's also different is this third zone has 4 wires (red,white,green,blue).
@Joe Mattiello what do you mean by "..see if board works normally."
0 -
0 -
@stanleegoodspeed
I would do what @Joe Mattiello suggested. Mark and disconnect all thermostat wires from the ZVC404.
Check and see if all zone valves are closed
Then get some jumpers or a scrap piece of wire. Jump out R & W for zone 1 and see if the valve drives open....take the jumper off the valve should close.
Then do the same think for zone 2 & 3
If they all work as they should reconnect zone 1 thermostat and see if it operates the valve open and closed.
then repeat for the other zones
If a zone works with the jumper or not with a stat then you may have found the issue
As @Joe Mattiello said you may need a resistor with that electronic stat0 -
@EBEBRATT-Ed thanks for the clarity, this is very helpful.
How do I check if the zone valve is closed? Turning on the heat and checking if the pipe is cold?0 -
There's a slide lever on those Honeywell zone valves. It's just underneath where the wires go into the operator. If it slides all the way over to the other end very easily, it's open.
It could be that the end switch on the two zone valves is no longer closing. Once the valve opens, it closes a micro switch in the zone valve that tells the zone valve control to turn on the boiler and the pump. It's what turns on the red light on the control. It's a common thing for end switches to fail and you have to replace the zone valve operator. You can buy them here.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
Hi
what do you mean by "see if board works normally?
When you've disconnected all thermostats and validate a demand using a jumper across RW on control one zone at a time, the board should open the valve, close the end switch interfaced with boiler RW terminals and fire the boiler. that's what I mean normal operating condition of ZVC control.
HAs this been resolved?
Joe Mattiello
N. E. Regional Manger, Commercial Products
Taco Comfort Solutions0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements