Help! How do I fill my in floor heating closed system?
bbauer
Member Posts: 2
How would you fill this type of in floor heating system set up?
0
Comments
-
I don't see any city water make up there so i suspect this is a glycol system
Does this system have antifreeze in it?
If it is antifreeze you going to need a pump.
If it just is water you can fill it by feeding water into the drain valve that you have the buckett under it. Use a regular garden hose and a female x female hose adapter (or a washing machine hose) bring it up to 12 psi. Yo will have to bleed the system0 -
Yes it is a glycol system in my shop. So I just need a pump and say a 5 gallon pale with the glycol/water mix, hook that up to the drain valve and pump it into the system? Do I bleed it from the pressure relief valve attached to the side of the boiler at the same time? If this is all correct that is.0
-
Do you know how much the system holds?
Either way buy a jug of glycol and you want a 50/50 mix of water and glycol you can buy premixed or mix your own but you have to pump a mix in so you know it's right.
Hook up your pump with some hoses and pump it in until you get the system to 12 psi
Take that automatic air vent off (above the boiler to the right with orange handle valve). Get a piece of tubing that will fit over that nipple the vent is on and attach the tubing with a hose clamp and run the other end of the tubing back into your bucket.
Now you need to get your circ pump running but don't let the boiler fire up. You will have to figure out how to do that. you cant fire the boiler until you have water in it and the system is bled
Run the system circulator, crack the bleed valve with your tubing on it to let air out. If the pressure in the system drops below 12 psi add more glycol.
Keep doing this until you get no bubbles out of the bleeder hose. then you should be ok1 -
unless the circulator has a check valve, it will not be an easy purge. I'd add a Webstone valve that allows you to isolate and fill/ purge at on point. A good air separator would also help, glycol is hard to get entrained air out of.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
That relief piping needs to be 3/4" not 1/2"
I hope your electric rates are real cheap!0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements