hello need help , I have a pennco steam boiler , it overfills to the point some water comes out of the radiator. Also at the same time it keeps turning off . Any idea what might be causing this?

0
Comments
-
Bypass though the boiler feed valves .. Manual or auto . Anything else connected to boiler like for hot water ?
There was an error rendering this rich post.
0 -
It will turn off because the water rising in the system increases the pressure, which turn the pressuretrol off. Good thing, too.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
If you have a tankless water heater coil in the boiler it may have sprung a leak or the manual feed valve is leaking by or if you have an automatic water feeder that could be leaking by0
Categories
- All Categories
- 87.6K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 429 Carbon Monoxide Awareness
- 124 Chimneys & Flues
- 2.2K Domestic Hot Water
- 5.9K Gas Heating
- 119 Geothermal
- 168 Indoor-Air Quality
- 3.8K Oil Heating
- 78 Pipe Deterioration
- 1K Plumbing
- 6.6K Radiant Heating
- 394 Solar
- 16K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements