HELP! I NEED SOMEBODY!
PlumbBob2075
Member Posts: 8
in Gas Heating
Guys… having a real pain in the **** time with this guy’s gravity fed system (NG boiler), he renovated and our company added a new radiator(small in size) to the 2nd floor addition, we relocated another(large in size) from one spot on the 2nd floor to another on the same floor, and we relocated a radiator(large in size) on the first floor about 5 feet. 3 radiators. 2 big, 1 small. 2 different floors. One gets hot(1f), one gets warm up to the valve and bottom 1/3 of radiator(2f large), one gets absolutely nothing(2faddition. I know this system is screwed, used to be steam, but this customer won’t let up and wants a solution yesterday. Really need help here.
0
Comments
-
Is it still gravity?
Gravity system's are pretty picky and any change of piping ESPECIALLY a reduction in pipe size will give you issues.
I am thinking you will need to convert it to a pumped system now.
0 -
Is this the same job posted here about a week ago?0
-
kcopp said:Is it still gravity? Gravity system's are pretty picky and any change of piping ESPECIALLY a reduction in pipe size will give you issues. I am thinking you will need to convert it to a pumped system now.0
-
EBEBRATT-Ed said:Is this the same job posted here about a week ago?0
-
It’s never gonna work as a gravity system with that pex the way it’s run.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
I like RIBs also, but sometimes a switching relay does make more sense. The RIBs need a box to mount to.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Here is the easiest way to solve the problems.
1. Add a circulator, probably the Taco 110 three piece pump or a Taco 0010 wet rotor pump.
2. Connect both returns with full size piping with a tee (at least 1-1/4" iron or 1-1/2" copper.
3. Cap off the unused return.
4. Wire the thermostat to a Taco SR501 relay T T terminals
5. Wire the burner circuit (where the thermostat used to go) to 5 and 6NO terminals on the SR501
6. Wire the circulator to 4NO and N (where N is the White wire)
7. Wire Hot to H and 3 (where hot is the Black wire)
This is how we did a circulator add-on back in the 1950s and 60s (way back when Help! I need Somebody was recorded by the Beatles)
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
1 -
I'm usually all for keeping a functioning old boiler, but that is just too old and too much of a change. you can make it work but that money would be better spent on a new boiler.
EDIT:
Just looked at your other post. i thought that snowman above was your boiler. You have a modern weil mcclain. That should convert to forced circulation nicely. Will need balancing valves to force the flow through the new pex, if you don't make it its own zone, at least bring it back to the boiler separately before the balancing valves for the former gravity loops.
Side note. somewhere you say something about a steam conversion. i think that system was always gravity hot water.1 -
A Taco 007F may work for you but be prepared to use a more powerful pump just in case.
I am familiar with Taco model numbers, but you can use Honeywell RA-845 relay or other brand, and another brand pump of equal capacity and performance. I'm just sure that what I specified will work in your situation even if it is a little overkill. The balancing valves may not be needed but are good to have just in case. Also add a ball valve below the pump so you can swap out the pump without draining the entire system.
I hope this helps.
Yours truly,
Mr. EdEdward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
1 -
mattmia2 said:I'm usually all for keeping a functioning old boiler, but that is just too old and too much of a change. you can make it work but that money would be better spent on a new boiler. EDIT: Just looked at your other post. i thought that snowman above was your boiler. You have a modern weil mcclain. That should convert to forced circulation nicely. Will need balancing valves to force the flow through the new pex, if you don't make it its own zone, at least bring it back to the boiler separately before the balancing valves for the former gravity loops. Side note. somewhere you say something about a steam conversion. i think that system was always gravity hot water.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements