Wet Return Line Size
fxrgrunt
Member Posts: 157
Good morning. My wet return was redone when the boiler was done before I lived in this house. It was done with copper but with no clean outs. I know copper is fine for wet returns but being I wanted to do clean outs anyways I may just install black pipe. My question is what size pipe would be proper for a wet return back to the boiler? My boiler is 150k btu. It runs to 2 separate 2" mains that are 66ft and 47ft long and drop down into the wet return on the end.
0
Comments
-
-
It depends on the load on the main that is connected to that wet return you are replacing.
Add up the EDR on that main
From the Burnham Heating Helper
Wet Returns
1" 900 EDR
1 1/4" 1530
1 1/2" 2430
2" 5040
You shouldn't use anything smaller than 1" on a wet return as they tend to plug up.
What is wrong with the pipe size yo have now?
2 -
-
EBEBRATT-Ed said:It depends on the load on the main that is connected to that wet return you are replacing. Add up the EDR on that main From the Burnham Heating Helper Wet Returns 1" 900 EDR 1 1/4" 1530 1 1/2" 2430 2" 5040 You shouldn't use anything smaller than 1" on a wet return as they tend to plug up. What is wrong with the pipe size yo have now?0
-
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements