flue gas condensation in boiler sections
santo
Member Posts: 2
Weil McLain GV 90+4 gas fired boiler showing signs of metal flakes in condensate p trap off of the recuperator. Factory mounted boiler controls have return water sensor set at 140F that will trigger the bypass circulator if water temp goes below that setting and will resume system circ as soon as temp goes above 140. If those metal flakes are the result of flue gas condensation ( condensation occurs around 130F ) I don't understand how that can happen with the control protections built into the system. What am I missing?
0
Comments
-
Have you verified that the sensor is reading accurately and that the bypass is turning on?
The condensation temp will vary a bit based on a few factors. Has a combustion analysis been performed? A boiler with poor combustion will have a higher or lower condensation point. The analyzer will also tell you the flue gas temp."If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
0
-
this is a new install. combustion check was performed and all seemed ok. I take that to mean that combustion temp was ok as well. return water sensor if ok0
-
@santo
If this is a new install I doubt any boiler deterioration. Maybe it was just a little debris form when the boiler was manufactured1
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 95 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 927 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements