What Caused Thread Damage?
Zman
Member Posts: 7,611
I came across this one today while investigating a regulator overpressure issue.
This aluminum regulator has stripped inner threads, the debris plugged the regulator and caused it to fail. The pipe was a factory threaded steel nipple and did not appear to be damaged. The contractor is a very experienced pipefitter, it is possible his apprentice did the work.
I am leaning towards either overtightening or poorly machined threads. Any thoughts?
This aluminum regulator has stripped inner threads, the debris plugged the regulator and caused it to fail. The pipe was a factory threaded steel nipple and did not appear to be damaged. The contractor is a very experienced pipefitter, it is possible his apprentice did the work.
I am leaning towards either overtightening or poorly machined threads. Any thoughts?
"If you can't explain it simply, you don't understand it well enough"
Albert Einstein
Albert Einstein
0
Comments
-
If that was factory installed then the knucklehead at the factory did something wrong. Bad tap at factory. If that was a field install part... then it is still a factory defect... that way you get a free one under warranty.
Tell the helper the 48" pipe wrench is a little overkill for 1/2" threadsEdward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
-
The chips are aluminum. I wondered about that. The female threads on the other side and the replacement look good. Mabe bad machining on the one."If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
@Zman
It's common for aluminum threads to gall. I have seen it many times on gas valves. Teflon tape with some anti seize on the tape and a very light brushing of anti seize on the inside threads is the fix
The reason you see this at the far end is if you DON't dope the inside with anti seize and just dope the outside threads the dope gets pushed off the end when the nipple is screwed in1 -
It doesn't look like the threads that were engaged are damaged in those pictures. Just the ones further in.
It doesn't look like galling to me and I wouldn't expect galling with steel and aluminum.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
1
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements