Mystery Valve
sasman
sasman Member Posts: 32
Have yet to locate any literature on this valve. It is on the large running end of that riser. These are the only pictures my tech could produce. Homeowner stated radiators started getting hot until he went down and "messed" with this valve. Some type of flow control but only a guess. My suspicion is what ever was inside that valve isn't there anymore.
Thanks guys.
    Jamie Hall Member Posts: 26,844
    Say what? Looks to me like a pretty ordinary swing check...
  • STEVEusaPA
    edited October 2021
    I thought we answered this on the other forum. If it wasn't you it was your tech. Are you in NC?
    "Its a straight pattern weighted lift check.
    Commonly called a flow control valve.
    The little flag there can be spun outward to allow for gravity flow should a pump fail.
    Typically not needed if there is only one pump for the system.
    Its typical function is to prevent off cycle flow on system with multiple pump circuits."
  • sasman
    Never got a clear answer on hvac-talk. Never got a clear answer on hvac-talk. Figured I see if these guys had any idea.
  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,686
    What Steve said.
    Retired and loving it.
    HVACNUT Member Posts: 7,235
    Now let's talk about that circulator. What is that?
  • Big Ed_4
    Big Ed_4 Member Posts: 3,364
    It's called a flow valve , or flow check . It prevents heat from rising up into the system when the circulator is off .
    EBEBRATT-Ed Member Posts: 19,605
    @sasman
    Just take it out and replace it with a new flow check.
    Just for your own information if you don't have DHW off the boiler and only have 1 zone you don't even need the thing
  • sasman
    The visible one is B&G. Wasn't there, "tech" that was; for 15 + years experience lacks rather much.
    There is another pump that I think is a small grunfoss, not real sure.