Hydraulic Separator physical placement
Peterug13
Member Posts: 8
I have a limited space install. Currently the plans call for the hydrosep to be mounted lower than the boiler and feed/return manifolds. About 12-14” lower but still lower than both. I’m wondering about the effectiveness of air removal in the HS being below everything. Should I put a second air scoop in the primary loop? Comments?
0
Comments
-
That will depend upon your Hydro-Sep. Alot of them have an air vent installed at the top for convenience of getting the air out of the hydro-sep and that's all. So in essence, yes, I would install an air separator
If your Hydro-Sep has a collision media inside, then you have an air separator already built in and do not need to add another.
Being below the boiler is irrelevant because all of the water/air has to pass thru it.
Dave H.Dave Holdorf
Technical Training Manager - East
Taco Comfort Solutions
3 -
Thanks Dave. Using a Taco Hydro-Sep. I’m going to include an air sep as well.0
-
I would not include a second air separator after spending the money on a hydraulic separator. I love those things but they are always massive and difficult to place in the system. In fact, where space is an issue, I don't use them at all. But they do a great job of eliminated both air and dirt and I've never made any effort to place one below the boiler and I don't know where that directive comes from.Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes1
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements