Secondary pressure backup for vaporstat
cdm
Member Posts: 77
On my 3 year old boiler installation, I have had to replace 3 Honeywell Vaporstats. I want to add a pressure control unit in series with the Vaporstat to shut down the boiler (if) or when the vaporstst fails. Maybe at 2 psi. Suggestions for a unit or switch to use as a safety.
cdm
cdm
0
Comments
-
Why did your vepourstats fail? I'll grant you that they get kind of unhappy over around 7 to 10 psi or so, but they should have shut the boiler off long before then.
Don't shoot the messenger. Find out why the vapourstats fail before you try to solve the problem.
Now as to a second (or even third) pressuretrol, that's quite common. In fact, it's recommended practice -- and in some installations it's required. I'd suggest a secondary pressuretrol set at perhaps 2 psi cutout with a 1 psi differential. That becomes your safety, and the vapourstat becomes your control, which is what it should be.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
PA404A Honeywell or Residio or whatever they call themselves now0
-
Thanks Jamie: I know Vaporstat should have shut down - but it didn’t ! Ed, thanks for the suggested pyrotrol 404-A, I’ll look into it.0
-
is the pigtail clear ?
is the pigtail present ?
picture of trol and pigtailknown to beat dead horses0 -
Neil’s: yes, yes and not a (trol) but a Vaporstat. Thoroughly checked out system - micro switch on vapostat stuck. cdm
switch is stuck0 -
badly overpressured. That will d oit. Or somebody pushed on it...cdm said:Neil’s: yes, yes and not a (trol) but a Vaporstat. Thoroughly checked out system - micro switch on vapostat stuck. cdm
switch is stuckBr. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements